Hi
Any idea why the UPS ( SUA3000RMI2U )was shutdown right away during lightning ( stormy weather ) but during regular black out UPS was normal it can back up more than 15 minutes.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:57 AM . Last Modified: 2024-03-18 03:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:57 AM . Last Modified: 2024-03-18 03:55 AM
The batteries are in good condition, we run self-test its ok, also we simulate power block out ( by unplugging from AC source ) with server load its seems ok.
Actually this not just happened to SUA3000RMI2U, it happened also to APC BX650LI-MS all ups is line interactive.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:57 AM . Last Modified: 2024-03-18 03:56 AM
Hi,
If the batteries were drained /low then the UPS would shut down. You should run a self-test to see if the batteries pass. I also suggest running a simulated power outage with a lamp plugged into the UPS and not essential computer equipment to see if the UPS sustains the lamp.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:57 AM . Last Modified: 2024-03-18 03:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:57 AM . Last Modified: 2024-03-18 03:55 AM
The batteries are in good condition, we run self-test its ok, also we simulate power block out ( by unplugging from AC source ) with server load its seems ok.
Actually this not just happened to SUA3000RMI2U, it happened also to APC BX650LI-MS all ups is line interactive.
Link copied. Please paste this link to share this article on your social media post.