Ask our Experts
Didn't find what you are looking for? Ask our experts!
Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Dear Everybody!
We try to upgrade UPS form SC620 to SMX750. In theory both have serial smart interface, so we need just replace UPS form old to new one.
But in practice SC has DB9 connector, SMX has RJ45 connector. Looks like this major difference, because PowerChuteBE handle it in a different way.
It is no way to configure UPS smart connector type, and no way to refresh/reinstall PowerChuteBE.
Therefore no way to upgrade from SC to (e.g.) SMX UPS!?
Our UPSs driven SLES servers.
Any idea?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Reinstall looks like work in test environment, I try to do it in a hot systems.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Hi,
What version of SuSE Linux are the servers?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Sorry, SLES 11.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Hi,
You should uninstall the version of PowerChute that is running, attach the serial cable that shipped with the SMT750 (SKU 940-0625), download the latest version of PowerChute from APC.com, and install the new version.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
On 4/12/2016 3:13 PM, Bill said:uninstall the version of PowerChute that is running
But there is no description (way) how to do this for linux/unix type operating system.
I found some description from windows, but is is useless for other kind of operating system.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Hi,
To remove PowerChute Business Edition open a terminal window and type sudo rpm -e pbeagent
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Reinstall looks like work in test environment, I try to do it in a hot systems.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.