Dear Everybody!
We try to upgrade UPS form SC620 to SMX750. In theory both have serial smart interface, so we need just replace UPS form old to new one.
But in practice SC has DB9 connector, SMX has RJ45 connector. Looks like this major difference, because PowerChuteBE handle it in a different way.
It is no way to configure UPS smart connector type, and no way to refresh/reinstall PowerChuteBE.
Therefore no way to upgrade from SC to (e.g.) SMX UPS!?
Our UPSs driven SLES servers.
Any idea?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Reinstall looks like work in test environment, I try to do it in a hot systems.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Hi,
What version of SuSE Linux are the servers?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Sorry, SLES 11.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Hi,
You should uninstall the version of PowerChute that is running, attach the serial cable that shipped with the SMT750 (SKU 940-0625), download the latest version of PowerChute from APC.com, and install the new version.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
On 4/12/2016 3:13 PM, Bill said:uninstall the version of PowerChute that is running
But there is no description (way) how to do this for linux/unix type operating system.
I found some description from windows, but is is useless for other kind of operating system.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Hi,
To remove PowerChute Business Edition open a terminal window and type sudo rpm -e pbeagent
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:29 AM . Last Modified: 2024-03-13 04:15 AM
Reinstall looks like work in test environment, I try to do it in a hot systems.
Link copied. Please paste this link to share this article on your social media post.