UPS settings or Powerchute settings?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS settings or Powerchute settings?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:48 AM . Last Modified: ‎2024-03-07 10:42 PM

0 Likes
4
2388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:48 AM . Last Modified: ‎2024-03-07 10:42 PM

UPS settings or Powerchute settings?

Hi there

I see a lot of help on these forums but haven't been able to find the answer I'm looking for. Sorry if it is somewhere and I haven't found it.
We got a client with a RT3000 with AP9617. I installed Powerchute Network Shutdown on the server to test. What I'm confused about is that if I log into the management card, I can set settings for times to send shutdown signals etc. And then when I log into the PowerChute window, I can also set shutdown events, etc. So let me see if I got this right.....
I set the UPS of when to send the shutdown signal (e.g. 10min before battery depleted).
At that point, with 10 min left, the UPS sends the signal to the servers to shut down.
The powerchute server receives the signal and checks its events.
If the event for battery discharged is set to shutdown, it does so. If the event is set to not shut down, it won't even though the UPS is sending the shutdown command.
Is that right?
I'm just a bit confused as to why there are settings on both sides.

Thanks
Alan

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:49 AM . Last Modified: ‎2024-03-07 10:42 PM

0 Likes
0
2388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:49 AM . Last Modified: ‎2024-03-07 10:42 PM

Hi there
Yea, thanks, that does explain it.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:48 AM . Last Modified: ‎2024-03-07 10:42 PM

0 Likes
0
2383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:48 AM . Last Modified: ‎2024-03-07 10:42 PM

Alan,

UPS: Battery Discharged is a completely different event with a completely different action. What you're looking at is the Low-Battery Duration, or what's commonly called the low battery signal time. With that much runtime remaining (we'll keep at your example of 10 minutes), the UPS sends a low battery signal to all the machines connected, stating to shutdown. Each PCNS client receives the shutdown command and begins a shutdown on itself. The UPS then begins its shutdown process if there is one configured on the NMC.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:48 AM . Last Modified: ‎2024-03-07 10:42 PM

0 Likes
0
2383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:48 AM . Last Modified: ‎2024-03-07 10:42 PM

I'm not sure there's a clarity of what the low battery signal is.


It's not an event within PCNS that can be configured for shutdown. Battery discharged is something that results from a failed self-test. That can be configured for a shutdown.

When the UPS reaches a low battery state (when runtime remaining = low battery duration) it will send out a shutdown command. This supercedes any shutdown setup that's already configured, as it's basically a "point of no return" for the PCNS client to shutdown gracefully or wind up having power cut to it.


Not sure if that clarifies it enough or not, please let me know.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:48 AM . Last Modified: ‎2024-03-07 10:42 PM

0 Likes
0
2383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:48 AM . Last Modified: ‎2024-03-07 10:42 PM

Hi. Thanks for the reply. Sorry, that was bad wording from my side. I meant the low battery signal.

But what I'm confused about is when the low battery signal gets sent out, and the PowerChute software receives it, will it shut the pc down irrespective of the settings in PowerChute, or only if the event in Powerchute is set to shutdown?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:49 AM . Last Modified: ‎2024-03-07 10:42 PM

0 Likes
0
2389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:49 AM . Last Modified: ‎2024-03-07 10:42 PM

Hi there
Yea, thanks, that does explain it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of