UPS back feed relay fault
  • UPS back feed relay fault
rovic
rovic
Cadet
Posted: ‎2025-01-06 05:46 AM
680
Hi Team,
I would like to ask for your support and expertise regarding on one of the UPS that I have. I am encountering a back feed relay fault for several times already from SMAR-UPS X 3000.
Do we have some workaround on this?
I am attaching the logs for your review.
Thank you in advance.
Kirk
Posted: ‎2025-01-06 07:02 AM
Based on the serial number this hardware is no longer covered by the standard APC warranty.
As such I’m hesitant to suggest a UPS Firmware Update. 🤦‍♂️
All the relevant information for updating the firmware can be found using this APC Resource Link:
https://www.apc.com/us/en/faqs/FA164737/
Regardless, the latest v15.X UPS firmware incorporates a few updates relating to power quality and sensitivity:
https://download.schneider-electric.com/files?p_Doc_Ref=Smart-UPS_FW_Release_Notes&p_File_Name=SMX10...
Once the hardware has been updated adjust the power quality, sensitivity, and transfer voltages.
NOTE: It’s very apparent this issue has been persistent for a very long time. As such the internal relays will be quite worn / damaged due to the endless open / close cycles.
The company / you should budget for a replacement unit in the near term. As the unit will fail declaring a relay weld error. Resulting in a drop load situation when you least expect it!
Questions Ask . . . 👍