Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
UPS VT Parallel Communications Kit
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2602:29 AM. Last Modified: 2024-03-1901:55 AM
UPS VT Parallel Communications Kit
We have 2 Smart UPS (SUVTP10kH2B2S) connected in parallel using the parallel kit (SUVTOPT009S). Recently had a main power module failure on UPS1, UPS 2 tokk over the load.
While installing the faulty power module unit of UPS1 and hooking up the parallel kit ,the UPS2 turned off the load. Which shouldn't happen. Load on UPS2 was then switched ON, disconnected the parallel unit of UPS1.
From the logs of UPS 2 just before the load was turned off i see this message "
UPS: A no master present fault exists in the parallel system.
However when checking found that one the 2 pins of the parallel kit got shorted (not inserting/fitting the parallel kit correctly). My query is
* does shortening of the pin will cause UPS2 to shutdown, if so why?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2602:29 AM. Last Modified: 2024-03-1901:55 AM
Hi,
I checked with the support team here in North America and they suggest you contact local support to get a field service engineer (FSE) on site. You should have local FSE onsite to download PM logs and verify which 2 pins where shorted on the parallel kit.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2602:29 AM. Last Modified: 2024-03-1901:55 AM
Hi,
I checked with the support team here in North America and they suggest you contact local support to get a field service engineer (FSE) on site. You should have local FSE onsite to download PM logs and verify which 2 pins where shorted on the parallel kit.
This is a heading
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.