Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-1212:44 AM. Last Modified: 2024-02-1410:12 PM
UPS Symmetra PX 250-500 SNMP Walk
Hi Community Expert,
We have a site install with a UPS Symmetra PX 250 - 500 (400kW).
When we perform a SNMP Walk with our powernetmib426, we found out there are few OID points information was confusing. Can we get the require information below from the SNMP Walk or we choose the wrong OID point. Please refer to the table below:-
S/N
Description
Attribute Name
OID
SNMP WALK
Return value
Remarks
1
Bypass system frequency
upsAdvInputBypassNominalFrequency
.1.3.6.1.4.1.318.1.1.1.3.2.8.0
NA
Available in MIB file,
Not Available in SNMP WALK Results,
Available in equipment display
2
Bypass current phase 1, 2 & 3
Not Available in MIB file,
Not Available in SNMP WALK Results,
Available in equipment display
3
Bypass system voltage phase 1, 2 & 3
upsAdvInputBypassNominalVoltage
.1.3.6.1.4.1.318.1.1.1.3.2.9.0
NA
Available in MIB file,
Not Available in SNMP WALK Results,
Available in equipment display
4
Bypass system total active power
upsAdvInputBypassTotalActivePower
.1.3.6.1.4.1.318.1.1.1.3.2.14.0
NA
5
Bypass system total apparent power
upsAdvInputBypassTotalApparentPower
.1.3.6.1.4.1.318.1.1.1.3.2.13.0
NA
6
The battery pack temperature measured in 10ths of degree Celcius
upsHighPrecBatteryPackTemperature
.1.3.6.1.4.1.318.1.1.1.2.3.10.2.1.5
NA
Available in MIB file,
Not Available in SNMP WALK Results,
Available in equipment display.
Please advise which is the right attribute for “Power system temperature power module”. Refer to the T&C report and UPS equipment display as attached.
7
The battery frame/cabinet temperature in tenths of degrees celsius.
upsDiagBatteryFrameTemperature
.1.3.6.1.4.1.318.1.1.1.13.3.2.1.9
NA
8
The battery frame/cabinet temperature in tenths of degrees celsius.