Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
UPS Runtime Remaining
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2907:04 AM. Last Modified: 2024-03-1204:46 AM
UPS Runtime Remaining
Hello, I have asmallproblem,we are a companyin charge of theover 460UPS.I havediscoveredthatI can change theexternal number of batteriesandevery timetheRemainingruntime changed. how can Iunderstandthetermcomputationalruntime Thank you
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2907:04 AM. Last Modified: 2024-03-1204:46 AM
Hi,
An APC Smart-UPS has a microprocessor which calculates runtime based on the load attached to the UPS and on its battery or batteries capacity. The calculation is based on battery / batteries Ah. When the battery or batteries are at 100% charge then the runtime will be X and when the charge is 50% then the runtime will be Y.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2907:04 AM. Last Modified: 2024-03-1204:46 AM
Hi,
An APC Smart-UPS has a microprocessor which calculates runtime based on the load attached to the UPS and on its battery or batteries capacity. The calculation is based on battery / batteries Ah. When the battery or batteries are at 100% charge then the runtime will be X and when the charge is 50% then the runtime will be Y.