Posted: 2021-06-26 12:54 AM . Last Modified: 2024-03-19 02:42 AM
Hello all,
Someone can help, I am connecting a new UPS Galaxy 5500 for the 1st time (This unit for the first time I mean), and during the commissioning paces I happened to measure the Rectifier output on the DC bus..gives 260VDC on open circuit (Battery Breaker OFF. The Battery bank is a 36 unit bank with12V batteries, nominal voltage 432VDC. I hesitated to connect the battery breaker QF1 on with such a disparity in voltage; is this normal?
Will the rectifier ramp up to the battery voltage? If not, will the battery higher voltage not damage the UPS/Rectifier?
Any ideas welcome and appreciated.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:54 AM . Last Modified: 2024-03-19 02:42 AM
On 8/20/2019 8:52 AM, Geofrey said:UPS Galaxy 5500
Its me again, just to add that the Unit is a 60kW capacity.
First time posting here and forgive if the topic or rules are not quiet perfectly followed by me yet
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:54 AM . Last Modified: 2024-03-19 02:42 AM
On 8/20/2019 8:52 AM, Geofrey said:UPS Galaxy 5500
Its me again, just to add that the Unit is a 60kW capacity.
First time posting here and forgive if the topic or rules are not quiet perfectly followed by me yet