Currently we are utilizing a Smart UPS 1000 SC on a system that pulls ~10Amps (1.1-1.2KW). The spec for the 1000 SC is 600Watts/1000VA. So my question is, "Is the 600 Watts total output power?" In other words am I asking for an overload situation? I had an overload over the weekend that shut my system down completely. This is the first time an overload has occurred using this model UPS in ~6 years. I have 4 of these systems (SCADA and PLC, SCADA alone pulls down 8A) in place using the same UPS. So now I am looking for root cause for the failure.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:08 AM . Last Modified: 2024-03-11 03:13 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:08 AM . Last Modified: 2024-03-11 03:13 AM
Thanks Voidstar. I assumed as much but was second guessing myself based on the idea that maybe the IT guy who purchased these knew what he was doing and that perhaps I was missing something. Again thanks for the response.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:08 AM . Last Modified: 2024-03-11 03:13 AM
>
The spec for the 1000 SC is 600Watts/1000VA. So my question is, "Is the 600 Watts total output power?" In other words am I asking for an overload situation?
>
Yes, 600 Watts and 1000 VA total is the maximum output limit. So equipment that draws ~1.1 kVA will overload that UPS. That said, if you got the 10A number from the equipment spec, it might be a worst-case number and the equipment might ordinarily draw less current.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:08 AM . Last Modified: 2024-03-11 03:13 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:08 AM . Last Modified: 2024-03-11 03:13 AM
Thanks Voidstar. I assumed as much but was second guessing myself based on the idea that maybe the IT guy who purchased these knew what he was doing and that perhaps I was missing something. Again thanks for the response.