UPS: Bypass not in range ; either frequency or voltage. happening more frequently?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS: Bypass not in range ; either frequency or voltage. happening more frequently?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:34 PM . Last Modified: ‎2024-02-29 11:54 PM

0 Likes
3
15115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:34 PM . Last Modified: ‎2024-02-29 11:54 PM

UPS: Bypass not in range ; either frequency or voltage. happening more frequently?

so im in to my first month at my new job and they gave me this to find out about.

they have told me that when ever they get this error that it it wont last longer then then like 15 mins or so but now its blowing up our email accounts.XQJjq8iJz5B%2BST3JC6YWpQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngXQJjq8iJz5B%2BST3JC6YWpQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

zl7wsApj3BThd2Zbj4lbjA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngzl7wsApj3BThd2Zbj4lbjA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

looks like the servers need 208 so cant move that up. eager to understand this better help fix the problem thanks!!!

Jason 

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:34 PM . Last Modified: ‎2024-02-29 11:54 PM

0 Likes
0
15102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:34 PM . Last Modified: ‎2024-02-29 11:54 PM

WOW thank you so much i can rap my head around it so much better now! i will start researching the acceptable power for the equipment attached and see what i can do next thanks again 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:34 PM . Last Modified: ‎2024-02-29 11:54 PM

0 Likes
0
15102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:34 PM . Last Modified: ‎2024-02-29 11:54 PM

Hi Jason,

In looking at your logs, I think this FAQ applies: http://www.apc.com/us/en/faqs/FA299053

Your input voltage is 240V but you are outputting 208V as shown in your screenshot. I understand what you said about the servers but keep in mind, if you're UPS goes to bypass, they will be fed 240V anyway.. this is not good practice in general and I believe is likely contributing to the alarms. I'll try to explain.

It seems like your max input voltage (Vmax) in the data log gets pretty close to the upper bypass voltage limit of 250V/ Frequency looks OK so I am betting it is the voltage triggering the alarm. It is trying to tell you, if the UPS has to go to bypass for one reason or another (fault, overload, etc), the voltage (or frequency) is out of the range. And depending on a few other settings and UPS model, it will turn off or feed this voltage/freq to your equipment.

To loop back, I think the main problem here is that your input and output voltage settings don't match. If your output was set to 240V and matched your input voltage, the bypass upper voltage would allow for a higher range and if the input voltage is going over 250V, it'd be within the limit based on 240V nominal (normal) voltage since the range could be changed to 270V.

I am reviewing the user's guide here for SRT3000 which according to your log is what you have. http://www.apc.com/salestools/JGNY-9LPDQJ/JGNY-9LPDQJ_R2_EN.pdf and refer to pg 15.

Note how the bypass voltage ranges change based on your output voltage setting. To address this, ideally you'd want to change your output voltage to match the input. I think modern servers and equipment can handle multiple voltages (120/208/240V) so if you want to pursue this, then you can investigate the acceptable input voltage ranges for the attached equipment connected to the UPS. This is usually indicated in the specs or on the power supply itself physically on the server. If you do find out the attached load can function at 240V, then you can probably change the output voltage setting. (You can only change the output voltage setting when the UPS is off.)

Alternatively, if the equipment is strictly 208V only for some reason, then you can also evaluate changing the voltage at the outlet/power feed to the UPS but I imagine that is not easy and will cost $$. 

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:34 PM . Last Modified: ‎2024-02-29 11:54 PM

0 Likes
0
15103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:34 PM . Last Modified: ‎2024-02-29 11:54 PM

WOW thank you so much i can rap my head around it so much better now! i will start researching the acceptable power for the equipment attached and see what i can do next thanks again 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:34 PM . Last Modified: ‎2024-02-29 11:54 PM

0 Likes
0
15102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:34 PM . Last Modified: ‎2024-02-29 11:54 PM

You're welcome!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of