Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
UNIFLAIR BREC1812 - Not Communicating over ModBus RTU
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2711:45 PM. Last Modified: 2024-03-1811:54 PM
UNIFLAIR BREC1812 - Not Communicating over ModBus RTU
Dear All,
We have installed BREC1812 UNIFLAIR Chillers in one of our project, we have installed ACAC76123 Serial Cards to communicate over RTU for our BMS System, however we are not able to communicate over the RTU, we have already configured ModBus Parameters for both Chillers.
Can someone please help us in identifying this issue.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2711:45 PM. Last Modified: 2024-03-1811:54 PM
Hello Waleed.
There are only a couple parameters on the unit to set for the Modbus.
SETTING TRANSMISSION PARAMETERS FOR SUPERVISION The following screen allows the basic parameters to be set (first three lines) for switching via supervision, i.e. 1. serial address of the unit connected to the serial supervision network (must match serial address set in supervision programme); 2. data transfer rate (Ser. speed): 1200, 2400, 4800, 9600 and 19200 for RS-485. (keep this at 9600 or 19200. 3. protocol type (standard or Modbus). (would be modbus in this case)
Some other things to try is to swap the wires on the card. Check is a resistor is needed at the end of the modbus chain. Try changing the parity on the Master to see if the values start reading. If these do not work, please call your local tech support to further troubleshoot the machines.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2711:45 PM. Last Modified: 2024-03-1811:54 PM
Hello Waleed.
There are only a couple parameters on the unit to set for the Modbus.
SETTING TRANSMISSION PARAMETERS FOR SUPERVISION The following screen allows the basic parameters to be set (first three lines) for switching via supervision, i.e. 1. serial address of the unit connected to the serial supervision network (must match serial address set in supervision programme); 2. data transfer rate (Ser. speed): 1200, 2400, 4800, 9600 and 19200 for RS-485. (keep this at 9600 or 19200. 3. protocol type (standard or Modbus). (would be modbus in this case)
Some other things to try is to swap the wires on the card. Check is a resistor is needed at the end of the modbus chain. Try changing the parity on the Master to see if the values start reading. If these do not work, please call your local tech support to further troubleshoot the machines.
Thank you