Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Trying to understanding 3 phase PDUs for a rack
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2605:25 AM. Last Modified: 2024-03-1901:02 AM
Trying to understanding 3 phase PDUs for a rack
I'm trying to get a layman's understanding to how 3 phase works for PDUs in a rack.
We are installing multiple blade server chassis in a rack and are trying to provide the necessary power/redundancy.
My general question is if I put in a 3 phase 208 30, 50, or 60AMP circuit/PDU into a rack (A and B side) how many Amps are available per phase (L1-L2 plugs, L2-L3 plugs, etc.).
I have read that it's 50amps per phase (really 80% of 50Amps per phase)
I've also read that it's 1/3 of 50Amps per phase (16.6 amps per phase)
If I look at APC's PDU data sheets it varies. A 3 phase 208 50 Amp 7.5Kw PDU says max of 20Amps per phase and the 12.5 KW PDU says 35Amps per phase.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2605:25 AM. Last Modified: 2024-03-1901:02 AM
usually their is a breaker on each bank. each bank references two of the phases. did you have any specific model in mind? we can check the breakers on it.
i am not that good with three phase power myself but i do handle the PDUs in general
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2605:25 AM. Last Modified: 2024-03-1901:02 AM
usually their is a breaker on each bank. each bank references two of the phases. did you have any specific model in mind? we can check the breakers on it.
i am not that good with three phase power myself but i do handle the PDUs in general