The snmp message "The UPS batteries are discharged" meaning?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The snmp message "The UPS batteries are discharged" meaning?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:17 AM . Last Modified: ‎2024-03-12 03:10 AM

0 Likes
3
6360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:17 AM . Last Modified: ‎2024-03-12 03:10 AM

The snmp message "The UPS batteries are discharged" meaning?


Hi, I'm brand new here. I'm tasked with monitoring about 500 SUA1000RMU2U's (and some similar 1500's). I commonly see errors like "The UPS batteries are discharged." In my thinking this would mean that they have been run down and had not had a chance to recharge, but it appears to more commonly indicate that the batteries are simply failing and require replacement. After sitting for a week being charged shouldn't it just recharge? Some of these units will toggle back and forth continually every 5 min. from the Discharged message to "The UPS discharge condition has been cleared." Sometimes the vertical row of charge lights are all blinking. They seem to pass the self test but then go right back to the Discharged messages. From your experience is this typically indicating a bad set of batteries, a battery connection/corrosion problem, or a charging circuit problem?  Is there a way I can tell without replacing the batteries if the charging circuit, the battery connections or the batteries are the cause? Thanks, Dennis

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:17 AM . Last Modified: ‎2024-03-12 03:10 AM

0 Likes
1
6361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:17 AM . Last Modified: ‎2024-03-12 03:10 AM

Hi Dennis,

I think you're ultimately seeing this -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US

Batteries discharged usually means that your reported battery runtime (how long the UPS can last on battery power) is within two minutes of your low battery duration - meaning your runtime is low. This can happen, assuming your low battery duration is at the default of two minutes, when the batteries are older and are in need of replacement because of overall diminished capacity. So if your reported runtime is 3 or 4 minutes, it'd report this basically telling you that you have older batteries and they cannot provide the same capacity they used to. They haven't failed the "self test" yet which would tell you to replace the battery flat out.

This can also happen if users increase their low battery duration to a non default value. Let's say 20 minutes. This means if you have 22 minutes of runtime, you'll see this alarm too. Some users do this for certain configurations since Low Battery is when the UPS starts telling PowerChute clients to shutdown. If all of the clients require 20 minutes to shutdown, it may make sense to do so but then you run into issues like this.

If you're not sure which it is, I can help you determine it if you pick a UPS doing it, let me know the reported runtime it says it can provide, and then provide me the event.txt and config.ini from the Network Management Card (which it seems you are using versus PowerChute). (Instructions here on getting the log files -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...) We can start there and I may have more questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:17 AM . Last Modified: ‎2024-03-12 03:10 AM

0 Likes
0
6361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:17 AM . Last Modified: ‎2024-03-12 03:10 AM


Hi, I'm brand new here. I'm tasked with monitoring about 500 SUA1000RMU2U's (and some similar 1500's). I commonly see errors like "The UPS batteries are discharged." In my thinking this would mean that they have been run down and had not had a chance to recharge, but it appears to more commonly indicate that the batteries are simply failing and require replacement. After sitting for a week being charged shouldn't it just recharge? Some of these units will toggle back and forth continually every 5 min. from the Discharged message to "The UPS discharge condition has been cleared." Sometimes the vertical row of charge lights are all blinking. They seem to pass the self test but then go right back to the Discharged messages. From your experience is this typically indicating a bad set of batteries, a battery connection/corrosion problem, or a charging circuit problem?  Is there a way I can tell without replacing the batteries if the charging circuit, the battery connections or the batteries are the cause? Thanks, Dennis

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:17 AM . Last Modified: ‎2024-03-12 03:10 AM

0 Likes
1
6362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:17 AM . Last Modified: ‎2024-03-12 03:10 AM

Hi Dennis,

I think you're ultimately seeing this -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US

Batteries discharged usually means that your reported battery runtime (how long the UPS can last on battery power) is within two minutes of your low battery duration - meaning your runtime is low. This can happen, assuming your low battery duration is at the default of two minutes, when the batteries are older and are in need of replacement because of overall diminished capacity. So if your reported runtime is 3 or 4 minutes, it'd report this basically telling you that you have older batteries and they cannot provide the same capacity they used to. They haven't failed the "self test" yet which would tell you to replace the battery flat out.

This can also happen if users increase their low battery duration to a non default value. Let's say 20 minutes. This means if you have 22 minutes of runtime, you'll see this alarm too. Some users do this for certain configurations since Low Battery is when the UPS starts telling PowerChute clients to shutdown. If all of the clients require 20 minutes to shutdown, it may make sense to do so but then you run into issues like this.

If you're not sure which it is, I can help you determine it if you pick a UPS doing it, let me know the reported runtime it says it can provide, and then provide me the event.txt and config.ini from the Network Management Card (which it seems you are using versus PowerChute). (Instructions here on getting the log files -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...) We can start there and I may have more questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

david.harfst
david.harfst
Cadet

Posted: ‎2024-06-13 08:21 AM

In response to BillP
0 Likes
0
4614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-13 08:21 AM

Negetive, Ghostrider.  I'm seeing this message repeatedly followed by a clear event a second later.  Batteries are only 1 year old (including in the attached extended battery pack) and the Output VA is only at 5.1%, 1.3 Amps.

This is a faulty sensor.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore