If I need to do a quick and dirty test to see if a Smart-UPS is functioning can I simply pull the UPS plug from the wall, check to make sure everything connected to the UPS is still running, and then plug the UPS back into the wall without first powering down the UPS?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 04:55 AM . Last Modified: β2024-03-08 03:51 AM
Yep, sounds about right.
According to the runtime chart for this unit, 31% load would be around 300-400 watts, so you should be getting around 33-51 mins runtime. I'd expect to get something in the middle there.
http://www.apc.com/products/runtime_for_extendedruntime.cfm?upsfamily=165
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 04:55 AM . Last Modified: β2024-03-08 03:52 AM
Thanks. Everything went smoothly. π When I performed the test the SUA 1500 was sitting at ~ 31% load. It lasted about 20 minutes before the battery hit ~ 50%. Does that sound about right?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 04:55 AM . Last Modified: β2024-03-08 03:52 AM
Yep. That is a perfectly reasonable test to ensure the UPS is working properly. You might hear UPS savvy people call it a "pull plug test" or "outage simulation". Regardless, APC support has customers do this all the time as a troubleshooting step.
You can plug the UPS right back in and it should switch back online, no interruption to the load.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-30 04:55 AM . Last Modified: β2024-03-08 03:51 AM
Yep, sounds about right.
According to the runtime chart for this unit, 31% load would be around 300-400 watts, so you should be getting around 33-51 mins runtime. I'd expect to get something in the middle there.
http://www.apc.com/products/runtime_for_extendedruntime.cfm?upsfamily=165