Testing of battery packs in Smart-UPS units

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Testing of battery packs in Smart-UPS units
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:43 AM . Last Modified: ‎2024-03-17 11:51 PM

0 Likes
1
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:43 AM . Last Modified: ‎2024-03-17 11:51 PM

Testing of battery packs in Smart-UPS units

It is my understanding that an APC UPS tests its batteries and calculates runtime by switching to battery, measuring how the voltage changes over time, and measuring other aspects of the electricity.  If it drops too quickly, this will trigger a bad battery notification.

With the new SRT models of the Smart-UPS Online series (replacing the older SURTA models), the battery packs have the same kind of connector as before, but seem to have some kind of in-band signalling. See, if you connect a battery pack to the SURTA, you have to update the battery pack count manually in PowerChute to update the runtime estimate.  With the SRT, when you plug in a battery pack, the LCD screen tells you it sees it, and even says it's updating the firmware, and then the runtime is updated automatically.

Does this new capability also introduce any new way for the equipment to tell you which battery pack has a bad battery?  By that I mean, if the Bad Battery LED on the SURTA appears, you had to disconnect all battery packs and add them back one at a time until the LED comes on again, to figure out which pack has the bad battery, then you can swap batteries to find out which battery in the pack is it.  I'm hoping the battery packs connected to an SRT can test their own batteries and identify their status individually to the UPS through this new data communications channel, eliminating all that manual work.

And is there anything else the new signalling capabilities between the SRT models and their battery packs can do?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:43 AM . Last Modified: ‎2024-03-17 11:51 PM

0 Likes
0
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:43 AM . Last Modified: ‎2024-03-17 11:51 PM

Hi Jeffrey,

Yes, the smart batteries used in the new SRT units allow the UPS to indicate which external battery pack is bad. It wont tell you which specific module within the pack, but it will isolate it to the pack. With that being said, our guidance is always to not mix old and new batteries and batteries in a single installation generally age at roughly the same rate since they are in the same environment, have had the same amount of use, etc etc...  This document address that:  http://www.apc.com/us/en/faqs/index?page=content&id=FA317828

As far as other features with the new smart packs - runtime reporting should be more accurate, setting the number of external packs is automatic, and there are intelligent temperature sensors in each external pack which will report back to the UPS to assist with temperature compensated battery charging. This will improve performance in "less than ideal" install environments.

Thanks,

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:43 AM . Last Modified: ‎2024-03-17 11:51 PM

0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:43 AM . Last Modified: ‎2024-03-17 11:51 PM

Hi Jeffrey,

Yes, the smart batteries used in the new SRT units allow the UPS to indicate which external battery pack is bad. It wont tell you which specific module within the pack, but it will isolate it to the pack. With that being said, our guidance is always to not mix old and new batteries and batteries in a single installation generally age at roughly the same rate since they are in the same environment, have had the same amount of use, etc etc...  This document address that:  http://www.apc.com/us/en/faqs/index?page=content&id=FA317828

As far as other features with the new smart packs - runtime reporting should be more accurate, setting the number of external packs is automatic, and there are intelligent temperature sensors in each external pack which will report back to the UPS to assist with temperature compensated battery charging. This will improve performance in "less than ideal" install environments.

Thanks,

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore