APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:17 AM . Last Modified: 2024-03-12 11:46 PM
hello my monitoring tool only shows a integer output of my temperature sensor.
Output now is 235 i want it like 23.5 celsius is this possible...
Hardware i use is APC PDU AP8659 & APC Sensor AP9335TH
OID i use is 1.3.6.1.4.1.318.1.1.26.10.2.2.1.8 from MIB powernet421.mib
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:17 AM . Last Modified: 2024-03-12 11:46 PM
Hello,
The description of this OID is: Sensor temperature reading in tenths of degrees Celsius which I do think you already understand.
This means that either you as the user or the SNMP tool you're using must know to move the decimal point over to provide the output as 23.5.
I don't think decimal responses are typically provided in SNMP based on the supported formats for numbers really only being integers, timeticks, etc so this is the norm that you usually need to transform the value to move the decimal place. Many SNMP tools I think also offer this capability to add a rule or something to move the decimal place for you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:17 AM . Last Modified: 2024-03-12 11:46 PM
Hello,
The description of this OID is: Sensor temperature reading in tenths of degrees Celsius which I do think you already understand.
This means that either you as the user or the SNMP tool you're using must know to move the decimal point over to provide the output as 23.5.
I don't think decimal responses are typically provided in SNMP based on the supported formats for numbers really only being integers, timeticks, etc so this is the norm that you usually need to transform the value to move the decimal place. Many SNMP tools I think also offer this capability to add a rule or something to move the decimal place for you.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.