Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Temperature Monitoring Only shows integer output
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2906:17 AM. Last Modified: 2024-03-1211:46 PM
Hello,
The description of this OID is: Sensor temperature reading in tenths of degrees Celsius which I do think you already understand.
This means that either you as the user or the SNMP tool you're using must know to move the decimal point over to provide the output as 23.5.
I don't think decimal responses are typically provided in SNMP based on the supported formats for numbers really only being integers, timeticks, etc so this is the norm that you usually need to transform the value to move the decimal place. Many SNMP tools I think also offer this capability to add a rule or something to move the decimal place for you.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2906:17 AM. Last Modified: 2024-03-1211:46 PM
Hello,
The description of this OID is: Sensor temperature reading in tenths of degrees Celsius which I do think you already understand.
This means that either you as the user or the SNMP tool you're using must know to move the decimal point over to provide the output as 23.5.
I don't think decimal responses are typically provided in SNMP based on the supported formats for numbers really only being integers, timeticks, etc so this is the norm that you usually need to transform the value to move the decimal place. Many SNMP tools I think also offer this capability to add a rule or something to move the decimal place for you.