Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. Based on the tech specs of the UPS - BR1500G-GR and Brochure. The UPS input frequency is auto-sensing, in the event that it goes above or below the threshold (50 Hz +/- 1 Hz, 60 Hz +/- 1 Hz) the unit will go on battery to provide the safe frequency.
The UPS's sensitivity can also be adjusted to accept a wider range of input voltage, you may refer to page 5 of the user manual.