Symmetra px 80kva setup battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra px 80kva setup battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
115
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:45 AM

0 Likes
9
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:45 AM

Symmetra px 80kva setup battery

Hi

I have a problem with an symmetra px that has lost the amount and type of betteries mounted to it......... How do I correct this ??

Kind regards

Henrik

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

Good day Henrik,

Let's make some things clear: you said the the UPS has stopped "seeing" the batteries, which means that the systems has worked before. second, I would be surprised if you have connected third party batteries, I am not sure you can do that on this model.
Now: check the comm cable between the UPS and battery( the rj-45 cable), check the rotary dial to be configured for the right number on battery cabs, check if the terminator is installed, ... also you might try to flash the card in order to refresh the communication between modules.
How old are the batteries, how many packs are phisycally presents, and check to be all of the same batch; usually they are identified by a letter and a number, make sure the things matches.
The UPS is smart and it sees recognizes immediatelly its environment..
Hope I could help...
take care
M

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:45 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:45 AM

I cant give you those files because im not at the unit now πŸ™‚

The thing I need is to know how I can get into the configuration of the unit ??

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:45 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:45 AM

hi henrik,

it'd be helpful to see the event log and other files available from the UPS to see what caused this and see exactly what the issue is.

can you provide the event.txt, data.txt and config.ini so i can help further? instructions are here -> http://nam-en.apc.com/app/answers/detail/a_id/9321

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:45 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:45 AM

where do you see this issue? powerview display? network management card? is it possible to provide a screenshot of what you see? thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:45 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:45 AM

I connected to the UPS via IP and noticed that the information wasnt there...... Also the UPS tells me a backup time that is not correct.

Im doing service on the UPS and before I can test it I need to get that information into the unit so the customer gets a more correct image of their backup time...

Kind regards

Henrik

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

well you can get these items remotely over a network connection to the NMC. but if you cant currently, i would say that 95% of the UPS configuration can be done within the network management card. i am not 100% sure on this UPS how it works with batteries so that is why i am questioning it. i have a PX40 in my lab and i am not sure of a way to tell it there are batteries since it should detect them automatically - that is why i am wondering if something else is causing the batteries to not show up.

if you log in via the web, all of your configuration is on the UPS tab.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

Tha batteries are external to the UPS so that can be why it wont detect them..... So it must be possible to tell the unit what type and size that is connected πŸ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

Cant remember if I have that option on the 80KVA...... But I will have a look the next time im up there πŸ˜‰

Do you know if there is a difference in the menues when you telnet ??

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

0 Likes
0
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

you should have it i think. and yes, telnet will be different. the web UI is the same between an AP9617/18/19 NMC1 or AP9630/31 NMC2 but the telnet interface is different. when you log in, if you get menu options, its an NMC1 and if there is just a blinking cursor and you can type commands, its an NMC2.

if AP9617 with a menu driven telnet interface, when you log in, go to 1-Device Manager, 1-Symmetra 80K, 3-Configuration, 4-General, 3-Batt Frame amp hours, and then enter the value in.then make sure you press 4-Accept Changes on that menu and it says success or your settings won't save and you'll need to do it over again.

if AP9630/31, you'll need to update this via the web UI or using a setting in the config.ini file and transfer it to the card since the option isnt available on the CLI yet.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 05:32 AM . Last Modified: β€Ž2024-03-19 12:44 AM

Good day Henrik,

Let's make some things clear: you said the the UPS has stopped "seeing" the batteries, which means that the systems has worked before. second, I would be surprised if you have connected third party batteries, I am not sure you can do that on this model.
Now: check the comm cable between the UPS and battery( the rj-45 cable), check the rotary dial to be configured for the right number on battery cabs, check if the terminator is installed, ... also you might try to flash the card in order to refresh the communication between modules.
How old are the batteries, how many packs are phisycally presents, and check to be all of the same batch; usually they are identified by a letter and a number, make sure the things matches.
The UPS is smart and it sees recognizes immediatelly its environment..
Hope I could help...
take care
M

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login