Symmetra RM Power Modules Error

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra RM Power Modules Error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:31 AM . Last Modified: ‎2024-03-08 02:28 AM

0 Likes
2
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:31 AM . Last Modified: ‎2024-03-08 02:28 AM

Symmetra RM Power Modules Error

Hi,

I have just started work at a site that has a Symmetra RM (model number AP9215RM) device. The unit has an error stating "no working power modules found – UPS in maintenance bypass”. There are 3 x Power modules and 3 x Battery modules inside this UPS. We have replaced one of the power modules with a spare (new) one but still the unit says it cannot find any working power modules.
any ideas?

thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:31 AM . Last Modified: ‎2024-03-08 02:27 AM

0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:31 AM . Last Modified: ‎2024-03-08 02:27 AM

Hi all,

I have similar problem with one power module from Symmetra LX. I changed old batteries with new batteries the same type (12V-9Ah), checked output voltage on black connector and there is ok, 135 Vcc. When I inserted this module in UPS appeared:

- First, after 5 seconds battery increased and display show total autonomy increased  with 8-10 minutes. This is ok until now. Main PCB see new module with batteries.

- Second, after 20 seconds appear error R3 power module fault on display and red led is on.

I tried to put this reconditioned battery module in other slot but appeared the same fault R4, R5...etc.

Inside PCB  from battery module is ok, no damaged...

What can be ?

Software problem ?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:31 AM . Last Modified: ‎2024-03-08 02:27 AM

0 Likes
0
2924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:31 AM . Last Modified: ‎2024-03-08 02:27 AM

Hi

To begin the AP9215RM is just the model of the LCD menu. The Symmetra RM's model and serial # would be on the back of the UPS.

This is probably going to be something where you need to call tech support. There could be a problem with an intelligence module in the system so it is not seeing the power modules.

I'd recommend calling in at 800-890-4272, if not, as long as you are in maintenance bypass (check the switch on the back), disengage all of the battery modules immediately. If the UPS sits in maintenance bypass for an extended amount of time, the batteries will discharge into the frame and become toast.

After removing the batteries, disengage all of the other modules and only insert the main intelligence module and then as long as you are in bypass,toggle the system enable switch (waiting 5 seconds in between) on the front. This will reset the UPS electronics only under normal circumstances. Then start the system with just that main intelligence module and then insert one module at a time after that, toggling the system enable switch each time, checking your error messages. Obviously, with only the intelligence module in there, you should get messages at that time like no good power modules, no batteries, etc. When you get to a power module, make sure its recognized and see if the issue is resolved. The main intelligence module might just need a reset or it might need to be replaced.

If you are not comfortable doing this, definitely call into tech support or perform this after hours. I only recommend the above procedure if you are familiar with the system and can perform this at your own risk.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:31 AM . Last Modified: ‎2024-03-08 02:27 AM

0 Likes
0
2925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:31 AM . Last Modified: ‎2024-03-08 02:27 AM

Hi all,

I have similar problem with one power module from Symmetra LX. I changed old batteries with new batteries the same type (12V-9Ah), checked output voltage on black connector and there is ok, 135 Vcc. When I inserted this module in UPS appeared:

- First, after 5 seconds battery increased and display show total autonomy increased  with 8-10 minutes. This is ok until now. Main PCB see new module with batteries.

- Second, after 20 seconds appear error R3 power module fault on display and red led is on.

I tried to put this reconditioned battery module in other slot but appeared the same fault R4, R5...etc.

Inside PCB  from battery module is ok, no damaged...

What can be ?

Software problem ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore