Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Symmetra RM 6KVA unit module slots query

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra RM 6KVA unit module slots query
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
CameronTQldAU
CameronTQldAU
Cadet

Posted: ‎2025-05-08 07:05 PM

0 Likes
0
299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-08 07:05 PM

Symmetra RM 6KVA unit module slots query

Hi, I recently purchased a new Symmetra rack chassis UPS solution. The channel partner/vendor recommended two Power Modules and five Battery Modules, so we followed that for the PO.

 

When I received the consignment and began assembly and initial pre-commissioning tests, I noted an unusual behaviour. I began by loading a Power Module into the L1 slot then powered up the frame. The Power Module was not detected. I powered down and moved the Power Module to slot L2 and powered up the frame again. This time the module was detected. I unboxed the second Power Module and plugged it into slot L1. Again, not detected. I placed the second Power Module into slot L3. Not detected. I swapped the Power Module in slot L2 with this Power Module. Module detected! (Ok, so neither Power Module is faulty). I placed the first Power Module into slot L3. Not detected. I placed this Power Module into slot L4. Module detected!.

 

Ok, so the two Power Modules are detected if are in slots L2 and L4, but not L1 and L3. Weird.

 

I placed the first Battery Module into slot R2. (the R1 slot contains the two Intelligence Modules, from the factory). Nope, the configuration and detection of the Power Modules in unchanged. I *did* find though, that when plugged the third Battery Module in (R4, with R3 already containing the second Battery Module and R2 still having the first Battery Module) that *now*, a Power Module in slot L1 *is* detected!

 

So my final configuration that was taken to the commissioning and Production workload environment was as follows: Power Modules in slots L1 and L2 and Battery Modules in slots R2-R4 and L3-L4.

 

Schneider Support seemed to be unable to provide any explanation to this behaviour of the slot interactions, nor any guidelines to the back-plane design other than what is in the standard instation instructions (ie, Power Module only for L1, Power Modules or Battery modules for L2 to L4, Battery Modules only for slots R2-R4)

 

I am wondering whether there would be success in powering up all slots if says we had bought only two Power Modules and two Battery Modules?  

 

So not an ongoing problem or issue for us now, but was just intrigued why the slots behaved in this manner. Has anyone else found similar situation?

regards

Cameron

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore