Symmetra RM 6000 - 5 faulty battery modules at once

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra RM 6000 - 5 faulty battery modules at once
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:23 AM . Last Modified: ‎2024-03-07 11:07 PM

0 Likes
1
809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:23 AM . Last Modified: ‎2024-03-07 11:07 PM

Symmetra RM 6000 - 5 faulty battery modules at once

Hello!

We have a Symmetra RM 6000 with the XR. 5 batteries on the MAIN and 3 on XR. 

We received an email alert after a self-test that at least one battery module is faulty. We checked the display and it was MAIN R2. A battery was ordered.

The display only listed one faulty - then said end of fault list hit ESC.

I pulled out R2 and noticed that it kept indicating a fault after I escaped from the message that the units of batteries were reduced. The warning message was for R3, so I reseat that one, then R4 said faulty. Then L3 and then L4. 

I thought this was over. But then it said 2 of the XR batteries were faulty. I reseat those. 

I was locked out of the management console since I've logged in with another device - could not get into it without resetting management card. I finally did that to gain access to the web interface. 

I did a self-test and it caused 4 of the batteries on MAIN to show faulty.

The XR did not show faulty - perhaps the self-test did not test XR. 

When I did a Google Search from the very beginning before I even knew 7 of the batteries were showing faulty, I came across a web article where someone had the same issue. I didn't think 1 hour later I would have ran into the same.

I am not sure where to go from here. I have a brand new battery... and now no use for it, unless I fill another slot. 

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:23 AM . Last Modified: ‎2024-03-07 11:07 PM

0 Likes
0
809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:23 AM . Last Modified: ‎2024-03-07 11:07 PM

I replaced the R2 battery anyway -- not happy with the replacement battery I got, it looks terribly beaten. 

But I did a self-test after that and it passed.

I don't think it would be normal for R2 to be faulty and trigger a fault with all of the other batteries... 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:23 AM . Last Modified: ‎2024-03-07 11:07 PM

0 Likes
0
810
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:23 AM . Last Modified: ‎2024-03-07 11:07 PM

I replaced the R2 battery anyway -- not happy with the replacement battery I got, it looks terribly beaten. 

But I did a self-test after that and it passed.

I don't think it would be normal for R2 to be faulty and trigger a fault with all of the other batteries... 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore