Does someone know what pulse-rectifier setting has the Symmetra PX? (160kW)
I'm trying to size properly a genset.
Thanks.
Message was edited by: fedelang
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:52 AM . Last Modified: 2024-03-19 01:19 AM
Does someone know what pulse-rectifier setting has the Symmetra PX? (160kW)
I'm trying to size properly a genset.
Thanks.
Message was edited by: fedelang
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:52 AM . Last Modified: 2024-03-19 01:19 AM
Thank you both. Here APC told us to use a 30% aditional overating in Genset. I used this: nominal output power + 10% of total nominal output power (battery chargers) then I applied a 95% efficiency factor by dividing the total load in 0.95 and then added a 20% to 30% margin. Of course there's still the critical services load such as chillers, condensers, fancoils,....
I recommend an electronic governor to control genset.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:52 AM . Last Modified: 2024-03-19 01:19 AM
Does someone know what pulse-rectifier setting has the Symmetra PX? (160kW)
I'm trying to size properly a genset.
Thanks.