Symmetra PX batteries

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX batteries
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:23 AM . Last Modified: ‎2024-03-19 02:24 AM

0 Likes
6
2596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:23 AM . Last Modified: ‎2024-03-19 02:24 AM

Symmetra PX batteries

What is the difference between the SYBTU1-PLP and the SYBTU2-PLP batteries (besides the cost)? Are they interchangeable?

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • battery
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:24 AM . Last Modified: ‎2024-03-19 02:24 AM

0 Likes
2
2596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:24 AM . Last Modified: ‎2024-03-19 02:24 AM

SYBTU1-PLP are for SUVT / G3500 / PX1

SYBTU2-PLP are for the PX2. 

The UPS won't recognise the batteries if the incorrect ones are inserted. As said above, SYBTU1-PLP are 7Ah, and the SYBTU2-PLP are 9Ah. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:23 AM . Last Modified: ‎2024-03-19 02:24 AM

0 Likes
0
2596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:23 AM . Last Modified: ‎2024-03-19 02:24 AM

Hello Bryan, 

Based off my experience with the Symmetra PX batteries, and the online spec sheet of the unit, there appears to be no difference within the batteries itself.  However, the battery module or casing that the batteries reside in may be different.  If you're doing a battery replacement, it may be more cost effective to purchase 12v9ah batteries from your local battery distributor.  They sell for ~$13.00 each, and from memory there are 8 batteries per module. 

Hope this helps!

-Eric

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:23 AM . Last Modified: ‎2024-03-19 02:24 AM

0 Likes
0
2596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:23 AM . Last Modified: ‎2024-03-19 02:24 AM

What I see is SYBTU1-PLP described as a "Symmetra PX Battery Unit" and has 7.2AH batteries inside. SYBTU2-PLP says "Symmetra PX 9AH Battery Unit, High Performance" so there are 9AH batteries inside those. They would be interchangeable as far as I can see, just depends how much runtime performance you'd want.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:23 AM . Last Modified: ‎2024-03-19 02:24 AM

0 Likes
0
2596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:23 AM . Last Modified: ‎2024-03-19 02:24 AM

If I may add to battery specifications comment - the 12v7.2ah battery was somewhat phased out years ago.  I believe if you search hard enough you may be able to locate them, however it would not be beneficial in any way.  The foot print of the 7.2, 7.5, 8.0, 9.0ah batteries are identical, in fact they are the same battery.  As Angela stated it will affect your runtime, but in a positive way.  More runtime is better! 

Bryan, as an FYI - batteries in series don't like to be mismatched. I suspect your question may be due to a battery alarm, or it may be time to replace battery(s). Try to keep the same age and spec of the battery within one entire module. 

-Cire/Eric

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:24 AM . Last Modified: ‎2024-03-19 02:24 AM

0 Likes
2
2597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:24 AM . Last Modified: ‎2024-03-19 02:24 AM

SYBTU1-PLP are for SUVT / G3500 / PX1

SYBTU2-PLP are for the PX2. 

The UPS won't recognise the batteries if the incorrect ones are inserted. As said above, SYBTU1-PLP are 7Ah, and the SYBTU2-PLP are 9Ah. 

Reply

Link copied. Please paste this link to share this article on your social media post.

chad.shipman
chad.shipman
Cadet

Posted: ‎2025-01-28 08:51 AM

In response to Anonymous user
0 Likes
0
1357
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-28 08:51 AM

This is only partially correct. The difference between these 2 packs are they have either 7ah batteries or 9ah batteries. You can convert a sybtu1 into a sybtu2 by changing the resister on the circuit board inside the pack. 

Reply

Link copied. Please paste this link to share this article on your social media post.

chad.shipman
chad.shipman
Cadet

Posted: ‎2025-01-28 08:58 AM

In response to Anonymous user
0 Likes
0
1357
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-28 08:58 AM

This is not correct. My PX500 can use sybtu1 and sybtu2 both. There is 2 difference in these packs. The 7ah or 9ah batteries and there is a resistor on the circuit board in the pack. You can change the R1, R2, OR R3 resistor (there will only one)

 

If you put 9ah Batts in a sybtu1 either the ups will reject it or use it as a 7ah battery causing you to lose the extra ah

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore