Symmetra PX 40k Output Shutoff without any log explanation

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX 40k Output Shutoff without any log explanation
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:42 AM

0 Likes
8
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:42 AM

Symmetra PX 40k Output Shutoff without any log explanation

Our Symmetra PX 40K shut off output for no apparent reason and the logs don't seem to explain why.  The unit is healthy and passed a self test a few days ago.  Its single cabinet unit without a bypass.

The log reports that a power event caused the output to shut off because it was in bypass. But as you can see, the unit never went to a bypass.   We did have a real outage and our other 40k went on battery and protected the load.

My question is it possible that during a failure event, the unit doesnt report all the events?   Notice we did get an alarm threshold during retstart.

=============

  • 08/18/2020    13:18:12           Device UPS: No longer in bypass.            0x011E
  • 08/18/2020    12:44:48         Device UPS: A load (kVA) alarm threshold violation no longer exists. 0x020A
  • 08/18/2020    12:44:29         Device UPS: The output power is now turned on.           0x0113
  • 08/18/2020    12:44:28         Device UPS: The power problem that caused the UPS to turn off while in bypass no longer exists.            0x0226
  • 08/18/2020    12:44:28         Device UPS: A load (kVA) alarm threshold violation exists.      0x0209
  • 08/18/2020    12:44:28         Device UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.     0x011C
  • 08/18/2020    11:41:42           Device UPS: The output power is turned off.      0x0114
  • 08/18/2020    11:41:42           Device UPS: An input voltage problem occurred while in bypass, turning off the UPS.    0x0225
  • <>
  • 08/13/2020    11:30:14           Device UPS: Passed a self-test.            0x0105
  • 08/13/2020    11:29:05          Device UPS: Started a self-test.            0x0137

 

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • px
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 12:47 AM . Last Modified: ‎2024-01-31 02:59 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:47 AM . Last Modified: ‎2024-01-31 02:59 AM

Hi Bob,

I don't think your going to get the level of support you require here for the three phase units, but if you log a request with the support team they'll be happy to help. I realise that your unit is out of warranty but that just means you won't get any components replaced, they'll still be able to help you with what's going on with the unit.

-Gavan 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-01-31 02:59 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-01-31 02:59 AM

From a quick look at the logs posted it looks like the unit seems to think it was in a by-pass state when the power went out, if it was then it is possible there will be no log of the actual issue but I'd recommend opening a case with your local support team so that we can do some deeper investigation.

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 10:12 PM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 10:12 PM

Thats what we thought too.  But the log would have mentioned it going to bypass by user, static switch, or forced bypass.    

We know that it cant pass a self test in Bypass mode, so just a few days ago it was online.

My theory is that during that instant of the outage, load surged, and for a moment we were at 151% load which would cause 1)bypass due to overload  2)shutdown due to power loss  and 3)alarm threshold notice.   But since it went down that instant it couldnt log those events.   Only when it came back online, did it send the alarm notice... but overload never came on.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 10:12 PM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 10:12 PM

I'm not 100% on the specs for the PX, but I don't think it can handle 151% overload for any length of time even in by-pass mode. If you provide the debug logs to the appropriate team they might be able to give you some more accurate information. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:42 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:42 AM

where do i find the debug logs

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-01-31 02:59 AM

0 Likes
0
3420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-01-31 02:59 AM

It depends on the NMC or PX brain but for NMC2 based products the link video below, but support will help you with gathering the logs for your particular unit:

https://www.youtube.com/watch?v=guo8BXKVFms

Reply

Link copied. Please paste this link to share this article on your social media post.

chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:42 AM

0 Likes
0
3420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:46 AM . Last Modified: ‎2024-02-14 02:42 AM

Data, Event, Dump, Debug attached... Doesnt look like much

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-07-12 12:47 AM . Last Modified: ‎2024-02-14 02:42 AM

0 Likes
0
3420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:47 AM . Last Modified: ‎2024-02-14 02:42 AM

Also.. can anyone translate SYMIM4 lights...

Looks like DIG1 D85 is lit red.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 12:47 AM . Last Modified: ‎2024-01-31 02:59 AM

0 Likes
0
3420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:47 AM . Last Modified: ‎2024-01-31 02:59 AM

Hi Bob,

I don't think your going to get the level of support you require here for the three phase units, but if you log a request with the support team they'll be happy to help. I realise that your unit is out of warranty but that just means you won't get any components replaced, they'll still be able to help you with what's going on with the unit.

-Gavan 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of