Posted: 2021-07-12 12:46 AM
This was originally posted on APC forums on 8/19/2020
Our Symmetra PX 40K shut off output for no apparent reason and the logs don't seem to explain why. The unit is healthy and passed a self test a few days ago. Its single cabinet unit without a bypass.
The log reports that a power event caused the output to shut off because it was in bypass. But as you can see, the unit never went to a bypass. We did have a real outage and our other 40k went on battery and protected the load.
My question is it possible that during a failure event, the unit doesnt report all the events? Notice we did get an alarm threshold during retstart.
=============
Posted: 2021-07-12 12:47 AM
This reply was originally posted by Gavan on APC forums on 8/21/2020
Hi Bob,
I don't think your going to get the level of support you require here for the three phase units, but if you log a request with the support team they'll be happy to help. I realise that your unit is out of warranty but that just means you won't get any components replaced, they'll still be able to help you with what's going on with the unit.
-Gavan
Posted: 2021-07-12 12:46 AM
This reply was originally posted by Gavan on APC forums on 8/20/2020
From a quick look at the logs posted it looks like the unit seems to think it was in a by-pass state when the power went out, if it was then it is possible there will be no log of the actual issue but I'd recommend opening a case with your local support team so that we can do some deeper investigation.
-Gavan
Posted: 2021-07-12 12:46 AM
This was originally posted on APC forums on 8/20/2020
Thats what we thought too. But the log would have mentioned it going to bypass by user, static switch, or forced bypass.
We know that it cant pass a self test in Bypass mode, so just a few days ago it was online.
My theory is that during that instant of the outage, load surged, and for a moment we were at 151% load which would cause 1)bypass due to overload 2)shutdown due to power loss and 3)alarm threshold notice. But since it went down that instant it couldnt log those events. Only when it came back online, did it send the alarm notice... but overload never came on.
Posted: 2021-07-12 12:46 AM
This reply was originally posted by Gavan on APC forums on 8/20/2020
I'm not 100% on the specs for the PX, but I don't think it can handle 151% overload for any length of time even in by-pass mode. If you provide the debug logs to the appropriate team they might be able to give you some more accurate information.
Posted: 2021-07-12 12:46 AM
This was originally posted on APC forums on 8/20/2020
where do i find the debug logs
Posted: 2021-07-12 12:46 AM
This reply was originally posted by Gavan on APC forums on 8/20/2020
It depends on the NMC or PX brain but for NMC2 based products the link video below, but support will help you with gathering the logs for your particular unit:
Posted: 2021-07-12 12:47 AM
This reply was originally posted by Gavan on APC forums on 8/21/2020
Hi Bob,
I don't think your going to get the level of support you require here for the three phase units, but if you log a request with the support team they'll be happy to help. I realise that your unit is out of warranty but that just means you won't get any components replaced, they'll still be able to help you with what's going on with the unit.
-Gavan