Symmetra LX and Cold Shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX and Cold Shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:47 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
6
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:47 PM . Last Modified: ‎2024-03-18 11:51 PM

Symmetra LX and Cold Shutdown

Hello,

Without AC input I cannot shutdown my UPS. I tried to press both buttons on the Intelligent modules for 4 seconds - (as the coldstart), but I cannot shut it down. Please advice me - how to do it quickly.

Rui

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

Right, there is no command you can give to the UPS to power down the intelligence modules instantly. As you discovered, you can command the load be turned off but the intelligence modules will remain alive for about 10 minutes with no AC and in Load Disconnect mode.

System Enable switch will instantly kill the intelligence modules and all other UPS electronics and take the load down if you aren't in maintenance bypass.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:47 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:47 PM . Last Modified: ‎2024-03-18 11:51 PM

Hello,

"Coldstart" is when you power up the UPS with no AC input, not powering it down.

I believe the "power off procedure" for Symmetra LX is actually printed on the rear of the UPS on a sticker for reference. You'd want to follow those instructions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:47 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:47 PM . Last Modified: ‎2024-03-18 11:51 PM

The instructions written on the rear of the Symmetra are made for a complete dismantle of the UPS.

That would be a silly thing - to disconnect all breakers / batteries / power modules - everytime I want to just shut it down. (sometimes just for 1 or 2 minutes)

Well, I noticed that after 10 minutes I clicked "output power OFF", it just shutdowns itself. But there must be a command somewhere to make it quicker (ex:5 minutes) or manually.

Best regards,

Rui

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

If you just want it to shutdown and don't care about "gracefully" shutting down the UPS, the easiest thing to do is flip the system enable switch on the rear of the UPS. This will turn off the load and UPS electronics. What you saw after 10 minutes is what happens to most of the APC UPSs - they "braindead" after ~10 minutes of no AC power input. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

Hello again Angela,

I know the "braindead" behaviour. I have a surt3000 and that is a common behaviour - l After (Test/Off) button is pressed, ups shuts down itself then a "click" is heard after 10 minutes. But on Symmetra LX - when you are working "On Battery", PowerView shows Status, etc.. If you choose Control > No AC Output, it mantains the UPS on standby mode. (And 10 minutes after it shuts down itself...)

Well, I'll have to check Powerchute commands in order to see where this flag (10 minutes) is defined and where this can be changed... or not ...(maybe it is a firmware thing)

Rui

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
0
1657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

What you're describing seems to be the normal behavior for something like Symmetra LX and cannot be changed. It is the equivalent for a UPS of this type to the SURT3000. The UPS braindeads all by itself. I think by flipping the system enable switch on the rear of the UPS, you'll have what you want.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
0
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

Right, there is no command you can give to the UPS to power down the intelligence modules instantly. As you discovered, you can command the load be turned off but the intelligence modules will remain alive for about 10 minutes with no AC and in Load Disconnect mode.

System Enable switch will instantly kill the intelligence modules and all other UPS electronics and take the load down if you aren't in maintenance bypass.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore