Symmetra LX SYPM4KP module repair / error 0040

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX SYPM4KP module repair / error 0040
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
119
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
dakotawallender
Crewman dakotawallender
Crewman

Posted: ‎2025-04-08 12:28 PM . Last Modified: ‎2025-04-08 12:28 PM

0 Likes
5
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-08 12:28 PM . Last Modified: ‎2025-04-08 12:28 PM

Symmetra LX SYPM4KP module repair / error 0040

Wondering if anyone has any insight on repairing the 0040 error on a SYPM4KP. I have 4 modules with this error that follow the main controller. i know that it is DC bus related but im not able to find any components that are defective yet. i can pull the DC fuses and it does not make a difference, but the error follows the controller.

 

Other known errors for those in need:

Error 8100: replace C6 and C11, 50v 35uf cap. bad will test OL.

Error 8000 repalce R266. known good measure 32.16K, bad OL. (on back side)

 

Full Raw:

0804 5B41 0040 2304

0002 08 9D 7C 05 00

00 00 4A BC 00 00

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-04-09 11:25 PM

0 Likes
2
726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-09 11:25 PM

Hello,

 

The fault appeared in this power module is output fuse fault ,we usually advise to replace the entire power module as this Power module is not field repairable and any other updates available in this forum regarding internal repair procedures inside the power module is not verified ,and it is not an authenticate information to rely on ,any hardware issue appeared in the power module, it is recommended to replace the entire power module beside we do not provide spare parts regarding the internal PCBAs inside this power module 

 

But I can give you a tip,you can open the power module,inside it the power main board 0P7447A,verify F3 and F4  (output fuse ) that is located inside  the output filter and current sense section PH1 and PH 2   beside  the inverter main section ,check the VOUT on these fuse ,if it is zero then F3 or F4  are  opened and needs to be replaced but I do not guarantee that this  is will repair the power module and regain back to normal operaion 

 

Please note that we do not recommend to repair these power modules onsite  and any consequences that might raise due to this repair is solely under your responsibility without any penalties or blame  on Schneider Electric ,we had of course internal documents that explain the repair procedures but is only for internal use by  our R&D team and it is not intended to be used by our internal SRs or authorized service partners for repair inside the power module 

 

We had ultraplan services that will guarantee the spare parts replacement  for break fix incase of failure that can be purchased to guarantee the proper repair of the unit 

 

Regards,

 

Karim

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-04-09 11:25 PM

0 Likes
2
727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-09 11:25 PM

Hello,

 

The fault appeared in this power module is output fuse fault ,we usually advise to replace the entire power module as this Power module is not field repairable and any other updates available in this forum regarding internal repair procedures inside the power module is not verified ,and it is not an authenticate information to rely on ,any hardware issue appeared in the power module, it is recommended to replace the entire power module beside we do not provide spare parts regarding the internal PCBAs inside this power module 

 

But I can give you a tip,you can open the power module,inside it the power main board 0P7447A,verify F3 and F4  (output fuse ) that is located inside  the output filter and current sense section PH1 and PH 2   beside  the inverter main section ,check the VOUT on these fuse ,if it is zero then F3 or F4  are  opened and needs to be replaced but I do not guarantee that this  is will repair the power module and regain back to normal operaion 

 

Please note that we do not recommend to repair these power modules onsite  and any consequences that might raise due to this repair is solely under your responsibility without any penalties or blame  on Schneider Electric ,we had of course internal documents that explain the repair procedures but is only for internal use by  our R&D team and it is not intended to be used by our internal SRs or authorized service partners for repair inside the power module 

 

We had ultraplan services that will guarantee the spare parts replacement  for break fix incase of failure that can be purchased to guarantee the proper repair of the unit 

 

Regards,

 

Karim

Reply

Link copied. Please paste this link to share this article on your social media post.

dakotawallender
Crewman dakotawallender
Crewman

Posted: ‎2025-04-10 04:03 AM

In response to KarimEissa
0 Likes
0
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-10 04:03 AM

Thank you for the reply. The DC fuses are good. The issue is in removable logic controller. I can take one from a good unit and put it in one of the 0040 modules and it will work fine and vise versa.

Reply

Link copied. Please paste this link to share this article on your social media post.

dakotawallender
Crewman dakotawallender
Crewman

Posted: ‎2025-04-10 04:08 AM

In response to KarimEissa
0 Likes
0
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-10 04:08 AM

One other note is if I raise the DC bus to 152v (12v higher than normal) the 0040 error clears and the module works. I have a bad intelligence module that boils the batteries but for this case it’s helpful in diagnosing 

Reply

Link copied. Please paste this link to share this article on your social media post.

KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-04-12 02:07 AM

0 Likes
0
663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-12 02:07 AM

Hello,

 

There is an issue appeared regarding MIM/RIM firmware 560 related to battery increase/decrease events and there is a new  firmware 562 is developed to resolve this issue so we recommends to replace both MIM/RIM modules to the latest version available that enhance the battery monitoring performance 

 

With IM FW v562, only the informational alarms will be suppressed from customer view, while actual failures/issues will continue to be displayed as usual. We believe that suppressing the informational alarm will not impact product performance or customer satisfaction. In order for the customer to view if the unit recognized the battery has been increased or decreased, please go into the battery section of either the NMC or the display and check the quantity reported.

 

Regards,

 

Karim

Reply

Link copied. Please paste this link to share this article on your social media post.

dakotawallender
Crewman dakotawallender
Crewman

Posted: ‎2025-04-14 06:47 PM

0 Likes
0
617
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-14 06:47 PM

Hello, I’m referring to the daughter board inside the power module not the IM. It seems to have an issue energizing one of the relays on the inverter board. On a daughterboard that works you can hear two relays energize right away and then another about a second later. With a 0040 board the 3rd relay that would come a second later is only a very soft click. I can remove the larger capacitors on the left side by the transformer and it doesn’t change the error. I have 4 of these modules with this issue so there is plenty of determination.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of