Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Symmetra LX 8KVA loud whistle/noise

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX 8KVA loud whistle/noise
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
5
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

Symmetra LX 8KVA loud whistle/noise

This morning my Symmetra LX 8KVA started making a loud whistling noise but it is showing no faults or anything different then usual. Normally it makes fair amount of noise, but this one can be heard through 2 walls and down the hall, and its not the alarm.
I've run the self diagnostic which passes, and there last event was auto self-test 6 days ago.

Any input on where to start troubleshooting this would be greatly appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 8kva
  • apc
  • noise
  • symmetra
  • symmetra_lx
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

hello..

i am going to assume you made sure you ruled out any other equipment making this noise? what i would guess, if it is actually the UPS, is maybe a power module. if you had redundancy, you could try pulling a module at a time to see if it stops when you remove any PM. if you do not have redundancy, the UPS would go into overload bypass though so if you are not sure if you have redundancy or not, you might want to verify that by checking the status menu on the UPS front display and see what it says. you can also check the network management card if its configured. you'd want at least N+1.

another idea is to try and put the UPS into maintenance bypass using the switch behind the UPS front cover to the right of the UPS powerview LCD, labeled as so. this would bypass the UPS inverters temporarily but keep the fans spinning on the power modules (which are the modules on the left side of the UPS labeled SYMP4KP. you could also try doing this to see if the noise stops.

before you touch it though, does anything ring a bell as far as adding some load the UPS, having a different load, removing some attached load, or installing any new parts?

if you have any questions before touching the UPS please let me know.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
1317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

lol glad you are all set.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
1320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

hello..

i am going to assume you made sure you ruled out any other equipment making this noise? what i would guess, if it is actually the UPS, is maybe a power module. if you had redundancy, you could try pulling a module at a time to see if it stops when you remove any PM. if you do not have redundancy, the UPS would go into overload bypass though so if you are not sure if you have redundancy or not, you might want to verify that by checking the status menu on the UPS front display and see what it says. you can also check the network management card if its configured. you'd want at least N+1.

another idea is to try and put the UPS into maintenance bypass using the switch behind the UPS front cover to the right of the UPS powerview LCD, labeled as so. this would bypass the UPS inverters temporarily but keep the fans spinning on the power modules (which are the modules on the left side of the UPS labeled SYMP4KP. you could also try doing this to see if the noise stops.

before you touch it though, does anything ring a bell as far as adding some load the UPS, having a different load, removing some attached load, or installing any new parts?

if you have any questions before touching the UPS please let me know.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

i am going to assume you made sure you ruled out any other equipment making this noise?
The UPS the only equipment in that room.
before you touch it though, does anything ring a bell as far as adding some load the UPS, having a different load, removing some attached load, or installing any new parts?
The noise started after I got in to the office this morning, and it can actually be heard from the lobby right now (the equipment room is down a short hall from the lobby), which isn't good.
what i would guess, if it is actually the UPS, is maybe a power module. if you had redundancy, you could try pulling a module at a time to see if it stops when you remove any PM. if you do not have redundancy, the UPS would go into overload bypass though so if you are not sure if you have redundancy or not, you might want to verify that by checking the status menu on the UPS front display and see what it says. you can also check the network management card if its configured. you'd want at least N+1.

another idea is to try and put the UPS into maintenance bypass using the switch behind the UPS front cover to the right of the UPS powerview LCD, labeled as so. this would bypass the UPS inverters temporarily but keep the fans spinning on the power modules (which are the modules on the left side of the UPS labeled SYMP4KP. you could also try doing this to see if the noise stops.
Its configured with 2 power modules and 3 battery modules, load at 40%, and fault tolerance is N+1.

What is the difference between the control panel activated bypass and the manual maintenance bypass?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

well the bypass option on the LCD is called command bypass where as the switch is more of a physical bypass that you control by operating the breaker. when you do command bypass, the UPS checks to make sure it is OK to go (voltage/frequency in range, etc). i also found some more info:

The manual bypass mode provides a no break transfer of load from inverter to bypass, or in other words it is a make-before-break transfer. Exiting from manual bypass to inverter involves a transfer time of 2-5msec and there is no check of the line voltage or other characteristics. Please keep in mind that when returning from maintenance bypass the Symmetra enters automatic bypass momentarily before attempting to transition to the online state.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

0 Likes
0
1317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:18 AM . Last Modified: ‎2024-03-11 02:43 AM

jparker wrote:
i am going to assume you made sure you ruled out any other equipment making this noise?
The UPS the only equipment in that room.
Scratch that, turns out someone installed and partly hidden a small budget UPS in the other corner of the room on a small phone system and it was making the noise. No idea it it was a fault alarm or not, but taken it out till someone admits to putting it there without tell me.

Thanks for the help, I actually would not have looked gone looking for a different source.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore