Symmetra LX 8000 RM Fail Over Time

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX 8000 RM Fail Over Time
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

0 Likes
9
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

Symmetra LX 8000 RM Fail Over Time

Hello,

   Im trying to limit how long the APC will be on during fail over and not sure how to go about it. Our AC unit is not on the APC so if we lose power and the systems fails over longer than 25 minuets we risk damage to our equipment due to overheating. Have any documentation or advise to restic the fail over going past 25 minuets? 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

0 Likes
0
2012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

Robert,

Which network management card do you have? If you have the AP9630 or AP9631 you may just have to upgrade the FW to get this feature.

That can be found here: http://www.apc.com/us/en/tools/download/index.cfm

If you have the much older cards, AP9617, AP9618, or AP9619 then I do not believe the early shutdown feature is on those cards. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

0 Likes
0
2012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

Hello Robert,

You can limit the amount of time the UPS runs on battery by accessing the network management card installed in the Symmetra. In the network management card you go to the "Configuration" tab and select "Shutdown". From here there will be a few different options to choose from under "Early Shutdown". One of the options is to shut off the UPS after it has been on battery for a specified time the user picks. Keep in mind that if you don't want your severs to just abruptly shut off when the UPS turns off then this may not be the most ideal configuration. The configuration to avoid that is to install and configure PowerChute Network Shutdown on the servers to allow them to perform a graceful shutdown. Once you have determined the last server that will turn off you can log into the PowerChute software on that server and select the option to "Turn UPS off". This will turn the UPS off once that last server finishes shutting down. Below is a link the the PowerChute Network Shutdown software and all documentation if you need it. 

http://www.apc.com/shop/us/en/products/PowerChute-Network-Shutdown-v4-2/P-SFPCNS42?isCurrentSite=tru...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

Our sysadmin doesn't want to use the PowerChute option, so going with early shutdown. I also dont see a specific option called "Early Shutdown" under Configuration>Shutdown, is this because I don't have a specific setting enabled or maybe different firmware?

Is there a way to change the variables in "Low Battery Duration" and "Shutdown Delay"? Currently can only select up to 20 minutes on the "Low Battery Duration" and 960 Seconds on the "Shutdown Delay". 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

Robert,

Which network management card do you have? If you have the AP9630 or AP9631 you may just have to upgrade the FW to get this feature.

That can be found here: http://www.apc.com/us/en/tools/download/index.cfm

If you have the much older cards, AP9617, AP9618, or AP9619 then I do not believe the early shutdown feature is on those cards. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:21 PM

Looks like the device is using AP9619, if we cant get the Early Shutdown tool is there a script we can run for this? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:20 PM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:20 PM

Hi Robert.

If you have an AP9619 installed and have access to it.

Select the UPS “TAB” then go to configuration > shutdown

Here you have the option to configure how your UPS will behave.

Regards,

Rich…

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:20 PM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:20 PM

Hi Robert,

It may be possible to do scripting if you are programming savvy. The older cards consisted of menu prompt Telnet. The newer cards were made more script friendly by having a command line interface Telnet. 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:20 PM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:20 PM

If you're interesting in scripting, I recommend either using SNMP or using Expect:

https://en.wikipedia.org/wiki/Expect

https://core.tcl.tk/expect/index

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:20 PM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:20 PM

Awesome, thanks for the resources! 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:20 PM

0 Likes
0
2013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:00 AM . Last Modified: ‎2024-03-07 10:20 PM

Found some information on this and looking into it now. Thanks much!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore