Hello, my Symmetra LX 16kVA (SYA16K16I) has failed. Can anyone give me any pointers?
There is no powerview (on MIM or RIM)
MIM has flashing green, steady red, flashing yellow, off, off
RIM has off, steady red, flashing yellow, off, off
We can hear relays clicking. no network management, no LOAD output, power module fans spin up, and then spin down
Removing the communications card clears the Red LEDS - put replacing the card doesn't fix and it still wont power up.
We have tried replacing the MIM and RIM from a working unit.
Any ideas? Tech are unsure of the fault.
Thanks
Adam
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:49 PM . Last Modified: 2024-03-18 11:50 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:49 PM . Last Modified: 2024-03-18 11:50 PM
The communications card suffered a bit of a whack, we have tried it with nothing connected including the network management card.
You don't happen to have a part number for the top backplane?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:49 PM . Last Modified: 2024-03-18 11:50 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:49 PM . Last Modified: 2024-03-18 11:50 PM
UPS was shutdown with no load, was moved to another floor, fault then appeared.
Power view is blank not backlight, no lights on powerview
Tried with management card inserted and removed, inserted - no lights, no network connectivity, cant login
All combinations of MINS and RIMS showed a steady red LED in the unit ie the known goods (the goods function fine in other unit)
Thanks
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:49 PM . Last Modified: 2024-03-18 11:50 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:49 PM . Last Modified: 2024-03-18 11:50 PM
The communications card suffered a bit of a whack, we have tried it with nothing connected including the network management card.
You don't happen to have a part number for the top backplane?
Thanks