Symmetra LX 16000 reports all batteries failed

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX 16000 reports all batteries failed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:35 PM

0 Likes
3
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:35 PM

Symmetra LX 16000 reports all batteries failed

I'm having a bit of a panic attack. We have 2 Symmetra LX 16000 and one of them suddenly shows all 9 battery modules as failed and reports Runtime Remaining: 0 minutes. I tried disconnecting and reconnecting all battery modules but after a few minutes all batteries are reported as failed. I also noted that in the overview you can see "Battery Capacity: 99%" which confuses me even more.

Is there anything that can be done? Can 9 battery modules fail simultaneously?

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • fault
  • smart-ups
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

What is your Actually Battery Dc bus voltage?  Also, do you have any internal temp faults in your logs?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

Hi Carlos. Very sorry for the delayed response. Typically, under normal circumstances if all the batteries are being used the same and are from the same batch (same age) then it is not impossible for them to all fail at once. It is not as common, but I have seen it before. How old are the batteries in question? Have they ever been replaced before? The event logs and a screenshot of the battery system from the NMC page showing serial numbers and mfg dates of the batteries would be helpful. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

I am not familiar with the LX, but in the Classic and RM Symmetra models, all communication happens over a single I2C bus and anything "hanging" that bus will generate lots of scary messages.

I'm just another user (I don't work for APC) but here is what I would do (assuming you don't have on-site APC support available):

Assuming your input power is clean enough and management policies allow it, I'd put the UPS in manual bypass, unseat all of the modules (MIM/RIM/PM/BATT) and unplug any communication cables from extended run cabinets (battery bus cables can stay connected). Then bring up a minimum configuration of MIM, 1 PM and 1 BATT. If the management interface indicates that this is a working config, then add items one at a time (first the RIM, then the PMs, then internal BATs, then external comms then external BATTs) until you either get the failure notice again or everything is working properly. Sometimes a simple remove/insert is enough to clear the problem.

Note that the minimum configuration is sufficient to start the UPS but is probably not enough to support your load - don't come out of bypass until you have everything reconnected and verified as working or you risk dropping the load.

A second note is that this procedure is ONLY for recovering from this specific condition. If you have a report of a single failed battery, don't remove and re-seat it in the hope it will get better. On the older Symmetra models the unit will mark it as good when it re-appears and you'll have the same thing the next time it does a self-test. On at least some newer Symmetra models, the UPS rewrites the SEEPROM in the battery module marking it permanently bad.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

0 Likes
0
1625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:59 AM . Last Modified: ‎2024-02-14 10:34 PM

What is your Actually Battery Dc bus voltage?  Also, do you have any internal temp faults in your logs?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of