Symmetra LX 16 RM - New Batteries won't charge

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX 16 RM - New Batteries won't charge
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

0 Likes
3
924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

Symmetra LX 16 RM - New Batteries won't charge

Hello,
We recently purchased new SYBT5 batteries and installed them into our 3 year old LX 16. The UPS does not seem to want to charge the batteries. They've been installed for weeks but they show a load of 16%, and a charge of 11%, with a 7 min run time. We had a 5 sec power outage the other day it took everything down. In the web-interface, in the "Overview" tab it says there is a battery fault. But in the "Status" tab it says 0 bad, 4 good for the batteries.

What should I do to get our UPS up and running?

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

0 Likes
0
923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

Ouch! 52.5V on the battery bus is not good. The nominal voltage is 120V on most (all?) Symmetras, with the actual voltage being somewhat higher, like 134V. I wouldn't expect the Symmetra to even be able to do a cold start with the battery bus that low.

Did you get your SYBT5's from an authorized APC distributor? Some outfits "refurbish" these modules, with varying levels of quality, and some even try to sell them as new. Unless the modules were drop-shipped to you by APC (a number of distributors don't keep stock of these modules on-hand for reasons I'll discuss below), they could be in "new" sealed APC packaging but still be quite old, if they were sitting in a warehouse for an extended period of time. Batteries will self-discharge over time, which may or may not be recoverable, depending on how long they were stored, the environmental conditions where they were stored, and what the voltage they're producing today is.

If you post the serial numbers here or contact APC technical support, they should be able to tell you how old those modules are. I'm just another end user, so I can't help you with that.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

0 Likes
0
923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

Thanks for the reply.

It's currently in Bypass, but it was online when we had the outage. Actual battery bus voltage is 052.5 VDC. We replaced all four of our SYBT5 Whole Modules.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

0 Likes
0
923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

Is the UPS currently online or in bypass?
What does it show for the battery voltage(listed as actual battery bus voltage)? show show this info under STATUS or detailed status
When you say you replaced the batteries, did you actually replace the WHOLE sybt5 or did you replace the 10 batteries inside each SYBT5?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

0 Likes
0
924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

Ouch! 52.5V on the battery bus is not good. The nominal voltage is 120V on most (all?) Symmetras, with the actual voltage being somewhat higher, like 134V. I wouldn't expect the Symmetra to even be able to do a cold start with the battery bus that low.

Did you get your SYBT5's from an authorized APC distributor? Some outfits "refurbish" these modules, with varying levels of quality, and some even try to sell them as new. Unless the modules were drop-shipped to you by APC (a number of distributors don't keep stock of these modules on-hand for reasons I'll discuss below), they could be in "new" sealed APC packaging but still be quite old, if they were sitting in a warehouse for an extended period of time. Batteries will self-discharge over time, which may or may not be recoverable, depending on how long they were stored, the environmental conditions where they were stored, and what the voltage they're producing today is.

If you post the serial numbers here or contact APC technical support, they should be able to tell you how old those modules are. I'm just another end user, so I can't help you with that.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of