Symmetra Extended frame fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra Extended frame fault
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:45 AM

0 Likes
8
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:45 AM

Symmetra Extended frame fault

I have one of the old Symmetra power array SY16KEXI with one additional battery frame. Since a week this shows message as "Extended Run Frame fault". The error message cleares itself in 20 secs "Extended Run Frame fault cleared". This happens few times a day. The battery frame communicaton is good and reports the right number of batteries and reports battery quantity increased and decreased messages. Is there are real problem with the extended frame or these are junk messages? The fault cleared message does not appear on the display but on the event long on the management cared (AP9606). Help me fix this.

Thanks.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

If it happens, I will keep you posted. Cheers.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

Bala,

I was a little confused by your post. Are you stating that only the 9606 reports that there is an XR Frame Fault? Have you gone through the powerview logs to see what they report? If the PowerView doesn't report anything, I would recommend reseating the 9606 and see if it continues. How old are the batteries in the XR Frame? I have attached a document if you would want to fill that out for us to do some small analysis. It's the standard PowerArray template.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

Hi there,

The power view also reports the same errors, but the fault cleared is reported in 9606 only and not in power view. I will try and get the form filled and sent to you. The batteries are 5-6 years old, but since the system runs with only very little load (10%), power view reports close to 5 hours of runtime and self test pass every fortnight.

Thanks
Bala

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

I had a similar problem with an Extended run cabinet - intermittant frame faults. The problem turned out to be the large DC bus connector that links the ups cabinet with the xr cabinet. There was a pointy looking "leaf spring" like contact in the middle of this connector (plugs into the bottom left corner of the rear panel of the Masterframe) that got slightly mashed at the ups end by the previous owner ( i bought it used). Check this connector for damage as it is fragile. Otherwise, you can also make sure you have the ferrite beads installed over the XR communications cable. Put a bead at both ends just to be on the safe side.

Good luck!
....Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

Thanks Dave. I reset the comms pcb where the battery comms cable pulgs in and after that the message dint popup yet ( 5 days now).

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

Bala,

Are you still going strong with this after reseating the CC?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

Yes, the error never appeared after that.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

Thanks for that update.

I'm curious to also know if you're planning on replacing the SYBATT's since they are beyond 100% life expectancy (as you stated that they are 5-6 years old).

If so, and they are going to be housed in the XR frame, can you let me know either here, or offline via Private Message whether or not you receive an XR Frame Fault or any other weird messages once replaced.


Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:35 AM . Last Modified: ‎2024-03-19 01:44 AM

If it happens, I will keep you posted. Cheers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of