Symmetra 80K has blown!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra 80K has blown!
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:02 AM . Last Modified: ‎2024-03-19 01:12 AM

0 Likes
0
540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:02 AM . Last Modified: ‎2024-03-19 01:12 AM

Symmetra 80K has blown!

Hi,

One of our Symmetra 80K UPS has blown. It blew all 3 160A fuses that sit inside the APC Power Distribution board. Looks like these fuses are for the Bypass feed. With the fuses blown, output failed yet the UPS still had power. I.e, all Power Modules were running, alerts were still coming in and the MIM and RIM had power.

We reckon the most likley cause of the fault was the Static Bypass Switch.

However, we've now replaced the Static Bypass Switch with a spare (moving the ID card with it). Have replaced RIM and MIM and installed a new PM. Removed all other PMs and all batteries apart from one row. It powers up without blowing the fuses but the MIM and RIM fail with red LEDs on both. Tried with just the MIM and get the same problem.

We've basically run out of ideas now. We've replaced as many modules as we can get our hand on. There are some small power supplies (fuses are ok) and a switch gear communication card that we haven’t replaced.

The error logs read:
UPS: The external switch gear communication card was removed.
UPS: The static bypass switch module was removed.
UPS: The load exceeds 100% of rated capacity.
UPS: A power module fault exists.
UPS: A main intelligence module fault exists.
UPS: A redundant intelligence module fault exists.
UPS: In bypass in response to an overload.
UPS: An Internal communication bus fault exists.
UPS: The output power is turned off.
UPS: The load no longer exceeds 100% of rated capacity.
UPS: A power module fault no longer exists.
UPS: No longer in bypass.


Interestingly the first log points to the switch gear communication. I've checked the card and there are no physical signs of damage. There's definitely no way this card could blow 3 phasse at 160A each! (or is there?)

Just wondering if anyone else has seen this fault and if yes, how they fixed it?

Also, if the switch gear communication card is blown, would that cause the MIM and RIM to fail to boot?

Thanks in advance for all advice and tips!

Glenn

Message was edited by: GSUK

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • apc
  • hardware
  • symmetra
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of