Symmeta UPC - Site wiring fault.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmeta UPC - Site wiring fault.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

0 Likes
4
737
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

Symmeta UPC - Site wiring fault.

Hello,

We just purchased a symmetra UPC, wired it over the weekend. At this point everything seems to be OK, other than the occasional Site Wiring Fault Message that keeps displaying on the LCD. Can anyone tell me what that means? I've tripled checked and had an electrician check the wiring.

thanks in advance!!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

0 Likes
0
738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

Hi,

We do not share schematics of APC products as they contain proprietary information. I am having trouble understanding what the issue is that you're asking about. I can share with you why a UPS reports a site wiring fault which that detail is here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA157507 

Furthermore, we have two varieties for Symmetra LX and there are two different power module models - SYPM4KP for North America use which does 208V or 240V 2ph, neutral and a ground and then there is SYPM4KI for international use - 220V/230V/240V. You can't mix and match those together as they are designed for different electrical environments.

Regardless, if you have further questions, please clarify what you're asking and share the exact model of UPS, input voltage setting, and power module part number(s) in use. Alternatively, you can also contact local technical support in your region for more specific assistance if you'd like.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

0 Likes
0
738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

Please see below;

http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7229&p_created=1124114838&p...

The Symmetra LX UPS system is designed to operate off nominal input voltages of either 208V or 240V consisting of 2 phases, a neutral and ground. Despite which nominal input voltage is supplied, 208V or 240V, the individual phase values should each be 120V. In the event that there is an 8% voltage difference between the 2 phases (i.e. phase (1) reports 120V and phase (2) reports 110V), the UPS will indicate “site wiring fault”. In the event that there is a 10% voltage difference between the 2 phases, the UPS will operate on battery power. To rectify the fault, the utility power will need to be addressed.

If the UPS does not detect a neutral, it will also report a site wiring fault.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

0 Likes
0
738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

I  am also confronting the same problem with APC Lx Symmetra.I have bought 4 in # APC LX symmetra having 2 phase +neutral+ground.

One guy reported me that he has set in order the same UPS and succeeded to operate on 230 V phase +neutral.I bought 3 in # UPS from that guy.Now the said 3 UPS are running OK but mine are not.I am an electronics engineering and compared for any diffirence or modification in the ciruit diagram.But I could not detect any modidfication.Might he chaged the software or else but I am still worried about my 4 in # UPS.I want to know the reason how the said guy made the UPS to run on 230 V +Neutral but I could do the same yet.

You are requested to kindly send me the diagram of the power module.I am sure that I would be able to run my UPS single phase +Neutral.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

0 Likes
0
738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

Further to my previous reply,pleaase send me the schematic diagram of Lx Symmetra power module 2phase +N+G on mty email ID     amanatalimr@gmail.com

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

0 Likes
0
739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:52 AM

Hi,

We do not share schematics of APC products as they contain proprietary information. I am having trouble understanding what the issue is that you're asking about. I can share with you why a UPS reports a site wiring fault which that detail is here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA157507 

Furthermore, we have two varieties for Symmetra LX and there are two different power module models - SYPM4KP for North America use which does 208V or 240V 2ph, neutral and a ground and then there is SYPM4KI for international use - 220V/230V/240V. You can't mix and match those together as they are designed for different electrical environments.

Regardless, if you have further questions, please clarify what you're asking and share the exact model of UPS, input voltage setting, and power module part number(s) in use. Alternatively, you can also contact local technical support in your region for more specific assistance if you'd like.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of