Symm LX batteries flagged bad prematurely during back-to-back outages. Ack!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symm LX batteries flagged bad prematurely during back-to-back outages. Ack!
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:41 AM . Last Modified: ‎2024-03-08 02:08 AM

0 Likes
2
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:41 AM . Last Modified: ‎2024-03-08 02:08 AM

Symm LX batteries flagged bad prematurely during back-to-back outages. Ack!

I have a pair of Symmetra LX Towers that are only 2 years old, sitting in a nice cool room. On saturday we had two successive unplanned power outages (3 hours apart) that both times completely drained the batteries (20 mins runtime on two SYBT5's per unit). According to the event log, right a the end of the second outage - fourteen seconds after the UPS turned off due to low battery - the ups's reported "UPS Battery Failure" and then one second later "Batteries require immediate replacement".

On the suspicion that maybe a few of the jars had gone bad in each module, I tore apart one of the SYBT5's, only to find that the voltages and internal resistances on all ten jars were fine. I did the same with a pack from the other LX, with same results...all jars were around 13.7 volts, no more than 100 milliohms resistance...most were at 85 milliohms. I have brand new Panny 12V 7.2 Ah cells that measure more than that. Yet, the UPS diagnostics menu is reporting "Weak Battery" for each and every SYBT5 module.

This brings up several big questions:

Firstly I am confused as to the timing of the battery fault, why would a pack be flagged as bad at the end of an on-battery operation, at a time when the batteries are totally drained and the UPS has no power ?

Why wouldn't the UPS firmware wait til power was restored, recharge the packs to full capacity and at the end or during that process determine if any modules are bad ?

Could this be an issue of the batteries not actually being fully re-charged after the first outage (even though the UPS data logs reported they were at 100% when the second outage hit, there was only three hours charging time), so the discharge was far more rapid the second outage (which is supported by the data logs) and the LX's processor falsely thought the packs were weak ?

Why are the packs being flagged as bad when my measurements show they are good ?!
( I have a B&K 601 tester ).

Also, I see the SYBT5 has an internal circuit board like Smartcells do. Is this board responsible for monitoring the health of the jars, and can it be reset like the smartcell board can ?

Cheers,
...Dave

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:41 AM . Last Modified: ‎2024-03-08 02:07 AM

0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:41 AM . Last Modified: ‎2024-03-08 02:07 AM

Thanks for your answer, I put in a case with tech support and have recieved a brand new set of SYBT5's already (under warranty). I will still look around to see how to reset the SYBT5...this was not a case of infant mortality - I am guessing the firmware on the UPS (MIM OS) is too strict with monitoring discharge curves of the cells. Yes, I tried disconnecting the string internal to the SYBT5 but nothing was reset.

Dave

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:41 AM . Last Modified: ‎2024-03-08 02:07 AM

0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:41 AM . Last Modified: ‎2024-03-08 02:07 AM

Battman -

i ran into a similar problem but was told that the batteries were not resettable at that time (possibly about a year ago). Did you call the TS line to see if they had any suggestions for resetting? (possibly pulling the batteries out and re-installing them one by one) the batteries sound like they are good to go, same measurements I would expect to see. What are the date codes on the batteries? they dont sound like weak jars so maybe its related to that chip inside....

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:41 AM . Last Modified: ‎2024-03-08 02:07 AM

0 Likes
0
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:41 AM . Last Modified: ‎2024-03-08 02:07 AM

Thanks for your answer, I put in a case with tech support and have recieved a brand new set of SYBT5's already (under warranty). I will still look around to see how to reset the SYBT5...this was not a case of infant mortality - I am guessing the firmware on the UPS (MIM OS) is too strict with monitoring discharge curves of the cells. Yes, I tried disconnecting the string internal to the SYBT5 but nothing was reset.

Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now