Switched Rack PDU:Communications lost.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Switched Rack PDU:Communications lost.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 07:04 AM . Last Modified: ‎2024-03-04 11:05 PM

0 Likes
3
2334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:04 AM . Last Modified: ‎2024-03-04 11:05 PM

Switched Rack PDU:Communications lost.

Hi we use your Switched Rack PDU's for our server room and have been getting notifications regarding this. What is the best course of action to take regarding this? It had the Er symbol as well.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap9730
  • ap9830
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:04 AM . Last Modified: ‎2024-03-04 11:04 PM

0 Likes
0
2334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:04 AM . Last Modified: ‎2024-03-04 11:04 PM

Well, we have a password reset procedure. That is a unit from 2003 whatever it is so it is likely that it will need to be replaced based on what you told me so far. Did you see the model number on the same sticker you got that serial number from?

Here is the password reset procedure for our AP79XX series Rack PDUs which I think you may have: http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156075 You'll need the serial cable/local connection for it in order to reset the administrator password.

I am not sure if you think it is worth pursuing the cable and resetting the password versus my educated guess/gut feeling that this device, based on age and symptoms, will need to be repalced.

Please let me know if you have any other questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:04 AM . Last Modified: ‎2024-03-04 11:05 PM

0 Likes
0
2334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:04 AM . Last Modified: ‎2024-03-04 11:05 PM

Can you confirm what model this is? It'd start with probably AP79 or AP89. The first several digits of the serial number would be helpful too. In general, this is not good and means the Network Management interface in the PDU has lost internal communication to other components of the PDU, such as the outlet relays. Reviewing the event log can help me determine that this is the case for sure though. 

This knowledge base has instructions on downloading the event.txt which I need -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 

Be advised if this error is because what I said, if the Switched PDU loses input power or is rebooted when communications are lost, it could cause the outlets to reboot or not turn on since the management interface and outlet relays can't "talk."

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:04 AM . Last Modified: ‎2024-03-04 11:05 PM

0 Likes
0
2330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:04 AM . Last Modified: ‎2024-03-04 11:05 PM

Hi Angela,

I'm having issues accessing the event info. The problem is I dont have the passwords to access the network card, no one in our office does since the person who set it up didnt share that info when he seperated the company. What do you recommend us to do in order to recover those passwords? As what info i have now i can just provide a serial number for the PDu since this is all the info i have plus its IP. I can give you all info once we can access our network card.

Serial # : WA0322160329

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:04 AM . Last Modified: ‎2024-03-04 11:04 PM

0 Likes
0
2335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:04 AM . Last Modified: ‎2024-03-04 11:04 PM

Well, we have a password reset procedure. That is a unit from 2003 whatever it is so it is likely that it will need to be replaced based on what you told me so far. Did you see the model number on the same sticker you got that serial number from?

Here is the password reset procedure for our AP79XX series Rack PDUs which I think you may have: http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156075 You'll need the serial cable/local connection for it in order to reset the administrator password.

I am not sure if you think it is worth pursuing the cable and resetting the password versus my educated guess/gut feeling that this device, based on age and symptoms, will need to be repalced.

Please let me know if you have any other questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of