Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84437members
353635posts

Switched PDU

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
179

Switched PDU

This question was originally posted by Luis Fernando on APC forums on 6/18/2015


Hi, I have an AP7900 Switched PDU, and I was wondering if it's possible to configure a sequential OFF triggered by an event of power loss in the UPS powering the PDU.

On the other hand, I want to know what triggers the ON and OFF Delay configured per outlet on the Configuration Tab?

Thanks.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
179

Re: Switched PDU

This reply was originally posted by Angela on APC forums on 6/18/2015


Hello Luis,

Yes, Power on/off delays under Configuration tab will apply when input power is applied to the PDU from a cold start  (like when the UPS powering the PDU turns off and back on again) and it also applies if you select the on-delayed or off-delayed commands within the PDU itself. You can bypass those if you select on-immediate or off-immediate.

I hope this clarifies. Let us know if you have further questions.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
180

Re: Switched PDU

This reply was originally posted by Angela on APC forums on 6/18/2015


Hello Luis,

Yes, Power on/off delays under Configuration tab will apply when input power is applied to the PDU from a cold start  (like when the UPS powering the PDU turns off and back on again) and it also applies if you select the on-delayed or off-delayed commands within the PDU itself. You can bypass those if you select on-immediate or off-immediate.

I hope this clarifies. Let us know if you have further questions.