Swapped AP9631 into an RMA'd Smart-UPS SRT 6000VA - Quick amber and unresponsive

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Swapped AP9631 into an RMA'd Smart-UPS SRT 6000VA - Quick amber and unresponsive
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

0 Likes
6
1636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

Swapped AP9631 into an RMA'd Smart-UPS SRT 6000VA - Quick amber and unresponsive

Hello, We have several of these Smart-UPS with the additional AP9631 card in them.

So a few days ago one of the units went bad and was boot looping, etc. We had it RMA'd and swapped it last night.

We moved the AP9631 card over but sadly it is unresponsive. If I plug in the console cable I get no feed back. If I hit or hold the reset button then the console/putty will give a garbled filled in box, but thats it. I tried holding reset for 60+ seconds, nothing.

Basically the lower right activity LED just blinks a fast steady amber. If I plug in ethernet, then the left blinks a few times, nothing special.

I noticed the UPS itself has a built in NIC. That was blinking alternate green and amber. I plugged the console into that and it came up right away.

Do I need to do something like disable the internal for the addon card to work? Am I losing any functionality with the internal vs AP9631?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

0 Likes
0
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

Can you look at this video and let me know if the flashing looks like this? https://youtu.be/VL-oQ9JKvP8 

If so, the AP9631 is bootmonitor mode and should be recoverable. It just may need a reflash of the firmware as it is in a recovery mode due to corrupt OS that can't boot (or some other similar issue). In this mode, you want to connect at 57600 baud rate instead and press enter a few times. It should say:

Rhodes Bootmonitor

BM>

I wouldn't be surprised when you do that, if you see AOS CRC failure on the screen or something like that.

From there, you'd want to basically follow these instructions: http://www.apc.com/us/en/faqs/FA293874

which you can skip up until 6 since you're in bootmonitor. Step 6 is where it explains how to begin loading the firmware. When you're in bootmonitor, you can do sysinfo and see what it says too and show me the output of that screen and I can tell you more specifically what is required.

All in all, we should be able to get you back up and running with this card I think.



See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

0 Likes
0
1638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

Can you look at this video and let me know if the flashing looks like this? https://youtu.be/VL-oQ9JKvP8 

If so, the AP9631 is bootmonitor mode and should be recoverable. It just may need a reflash of the firmware as it is in a recovery mode due to corrupt OS that can't boot (or some other similar issue). In this mode, you want to connect at 57600 baud rate instead and press enter a few times. It should say:

Rhodes Bootmonitor

BM>

I wouldn't be surprised when you do that, if you see AOS CRC failure on the screen or something like that.

From there, you'd want to basically follow these instructions: http://www.apc.com/us/en/faqs/FA293874

which you can skip up until 6 since you're in bootmonitor. Step 6 is where it explains how to begin loading the firmware. When you're in bootmonitor, you can do sysinfo and see what it says too and show me the output of that screen and I can tell you more specifically what is required.

All in all, we should be able to get you back up and running with this card I think.



Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

0 Likes
0
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

Sorry, forgot to add that the internal NIC is just fine to use. Adding an AP9631 is mostly redundant and you can maybe use this NMC in a different UPS. Major differences I think would be the number of UIO ports for accessories like dry contact or temp sensor (1 port on internal NMC I believe, 2 on AP9631). And I forget if the SRT6K would have a USB port on the back like the AP9631 does which can do firmware upgrade. But that may be a difference too. Other than that, no differences - same firmware, functionality, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

0 Likes
0
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

Yes, that appears to be the case, it's in bootmonitor mode.

I did a sysinfo,

Model        : AP9631
MAC Address  : xxxxx
Serial Number: xxxxx
CPU Speed    : 200
Link Port    : 3
Warmstart    : YES  NMI Count: 0

*********** FLASH MODULE INFORMATION *****************

Boot Monitor :
  Name       : apc_hw05_bootmon_108.bin
  Version    : 108
  Cookie     : 963200
  Build Date : Apr  8 2014
  Header Crc : A9D5(PASS)
  Module Crc : 9897(PASS)

AOS          :
  Name       : apc_hw05_aos_646.bin
  Version    : 646
  Cookie     : 963201
  Build Date : Oct  6 2016
  Header Crc : 3117(PASS)
  Module Crc : 39EA(FAIL)

APP          :
  Name       : apc_hw05_sumx_646.bin
  Version    : 646
  Cookie     : 963201
  Build Date : Nov  2 2016
  Header Crc : 2603(PASS)
  Module Crc : 70CB(PASS)

MTO          : Not Present

LPK          : Not Present

So by the looks of it the AOS went bad? Updated with 6.56 version and unit came up, configuration still seemed intact.

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

0 Likes
0
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

OK, great! Glad you were able to recover.

Yes, something happened here to cause the AOS to become corrupt since you can see the module CRC as FAIL in the sysinfo. I have seen this before when the UPS the NMC is inside of loses power abruptly, though I have never seen it personally or when removing the NMC from power in trying to simulate it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

0 Likes
0
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

Well that is sort of what happened. The main unit died, was throwing some errors, internal hardware failure, etc. It would stay on about 35-40 seconds, make a physical click sound, reboot, and repeat.

So it was put into maintenance mode remotely to stop the alerts, but its possible between then and when we finally removed it, it did cause damage. It was like that approx 14 days before we had the rma unit and had the scheduling to replace it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

0 Likes
0
1637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:30 AM . Last Modified: ‎2024-02-15 12:16 AM

Ahh. OK, I don't exactly know why but I wouldn't be surprised of that scenario contributed to the corrupted AOS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore