Staggering power-on after a coldstart.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Staggering power-on after a coldstart.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-18 04:26 AM

0 Likes
2
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-18 04:26 AM

Staggering power-on after a coldstart.

Hi,

We are installing 4 new circuits (3 phase, wye, 208V) and are thinking of using the AP7991 PDU.

One question:
1) On coldstart, is there a way to sequence the power to each outlet such that we do not blow a break if they all turn on at the same time? I have read the docs at (http://www.apcmedia.com/salestools/ASTE-6Z6KAV_R1_EN.pdf) and understand we can set the "Power On Delay", but it was not specifically stated that this delay is used (per outlet) on a coldstart.

My concern is exaberated since one of APS's competitors says that this is not the case- that the APC unit can NOT be setup to stagger power-on after a cold-start. (IE. They are saying that the "Power On Delay" only applies during manual/web interface restarts.)

Some details would be very helpful.

Thank You,

Joel

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-18 04:26 AM

0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-18 04:26 AM

I configure that by Device Manager -> Configuration :

Name Power On Delay Power Off Delay Reboot Duration
1 Outlet 1 5 Seconds Immediate 15 Seconds
2 Outlet 2 10 Seconds Immediate 15 Seconds
3 Outlet 3 15 Seconds Immediate 15 Seconds
4 Outlet 4 20 Seconds Immediate 15 Seconds
5 Outlet 5 25 Seconds Immediate 15 Seconds
6 Outlet 6 30 Seconds Immediate 15 Seconds
7 Outlet 7 35 Seconds Immediate 15 Seconds
8 Outlet 8 40 Seconds Immediate 15 Seconds

After a coldstart, each outlet start every 5 secondes...
--
Mensa

Message was edited by: mensa

Message was edited by: mensa

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-18 04:26 AM

0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-18 04:26 AM

I believe that you will able to configure what you want under Device Manager->Configuration menu. also, I can tell you that you can schedule reboots of the outlets and set a "Power on delay" for that too if you needed to do a daily reboot or power cycle to the pdu.

there is also a command line interface that you can set up to possibly run a script to do something like this - i will attach the document on those commands to this post.

We also have a website, http://testdrive.apc.com, where you can log into a real live switched rack pdu and check out your options there. You can go to the Device Manager tab->Configuration menu inside the pdu and either configure specific outlets or groups of outlets to have a "Power on delay."

Try logging into http://159.215.9.33/ with a username of apc and a password of apc and see what you think about what I mentioned. dont forget to check out the attachment on the command line information if you needed to go that route.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-18 04:26 AM

0 Likes
0
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:33 AM . Last Modified: ‎2024-03-18 04:26 AM

I configure that by Device Manager -> Configuration :

Name Power On Delay Power Off Delay Reboot Duration
1 Outlet 1 5 Seconds Immediate 15 Seconds
2 Outlet 2 10 Seconds Immediate 15 Seconds
3 Outlet 3 15 Seconds Immediate 15 Seconds
4 Outlet 4 20 Seconds Immediate 15 Seconds
5 Outlet 5 25 Seconds Immediate 15 Seconds
6 Outlet 6 30 Seconds Immediate 15 Seconds
7 Outlet 7 35 Seconds Immediate 15 Seconds
8 Outlet 8 40 Seconds Immediate 15 Seconds

After a coldstart, each outlet start every 5 secondes...
--
Mensa

Message was edited by: mensa

Message was edited by: mensa

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore