Some questions on battery backup load and how it's calculated when the UPS is turned on

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Some questions on battery backup load and how it's calculated when the UPS is turned on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
mapc_apc
Crewman mapc_apc
Crewman

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

0 Likes
4
1854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

Some questions on battery backup load and how it's calculated when the UPS is turned on

Can anyone please explain how maximum load on battery backup is calculated?

Let's use BACK-UPS ES - BE850G2-UK UPS as an example, it's 520W to which I want to connect an OLED TV(150W), a PS4 Pro(310 W) console and a PS3 slim console(110 W) for a total of 570W, more than the device can support.

If I do go ahead with this setup, will the UPS beep due to overload as soon as I turn it on or it will only complain the moment all three devices are switched on and using maximum power?

For example, if the TV is on (150W), the PS4 Pro is on(using its full power 310 W) but the PS3 console is turned off(1W), meaning that I am technically using 460W out of the possible 520W, will the UPS complain? And if it does, will it simply shut down or will I have a couple of minutes time to properly turn off my devices before turning the UPS shuts down?

And finally, why is PowerChute showing that it's not recommended to connect more devices to the battery backup in this video? https://youtu.be/n9omkITPn28?t=101

According to the screen it seems that this user is using 350W out of a possible 540W so why the warning?

Thank you.

Labels
  • Labels:
  • General Questions & Suggestions
  • Tags:
  • battery_backup
  • load
  • PowerChute
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

0 Likes
0
1854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

1) It will only complain once it goes past it's maximum power output or gets very close to it.

2) I can't say for certain what will happened when the UPS is on mains different units behave different ways but on battery the UPS will turn itself off straight away if it is overloaded by that much.

3) There is lots of reasons why it is recommending not to add any more devices some might be:

  1. Peak power
    • A PC with a 450 watt power supply might only use 50 watts on the desktop but 200 watts playing video
  2. Time on battery
    • A UPS that only lasts 30 seconds might be useless, pushing it to it's limit will mean that the battery will have a very short run time.
    • For the unit above the run-time looks like this: 
      050w: 79 mins
      100w: 35 min
      200w: 13 min
      300w: 7~ min
      400w: 3.5 min

-Gavan

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

0 Likes
0
1855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

1) It will only complain once it goes past it's maximum power output or gets very close to it.

2) I can't say for certain what will happened when the UPS is on mains different units behave different ways but on battery the UPS will turn itself off straight away if it is overloaded by that much.

3) There is lots of reasons why it is recommending not to add any more devices some might be:

  1. Peak power
    • A PC with a 450 watt power supply might only use 50 watts on the desktop but 200 watts playing video
  2. Time on battery
    • A UPS that only lasts 30 seconds might be useless, pushing it to it's limit will mean that the battery will have a very short run time.
    • For the unit above the run-time looks like this: 
      050w: 79 mins
      100w: 35 min
      200w: 13 min
      300w: 7~ min
      400w: 3.5 min

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

mapc_apc
Crewman mapc_apc
Crewman

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

0 Likes
0
1854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

Hi Gavan.

Thanks for the reply, very helpful!

So if I understood correctly, if I make sure to keep the PS3 turned off when using the PS4 Pro and if the PS4 Pro as well as the TV are using their peak power, I should be safe as I'm using 460W out of the possible 520W.

Alternatively, I could play it safe by opting for a bigger UPS even though in my specific case I would prefer to stick to two BACK-UPS ES because they are not IEC C14.

In that case, having made my calculations with additional devices connected to the two UPS, can you please help me understand the battery runtime for these two units since the runtime charts on the APC website are only for the Smart products:

Backup ES 850VA
Load: 404W (out of a possible 520W)

I know it's 6 minutes for 350W(using https://www.amazon.co.uk/dp/B0828G42KN) so with 404W we're looking at maybe 3 minutes?

Backup ES 700VA
Load: 260W (out of a possible 405W)

Maybe here we're looking at 6 minutes?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

0 Likes
0
1854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

The numbers above are for the 850, as for the 700 it's:

050w - 43.5 mins

100w - 21.5 mins

200w - 08.5 mins

300w - 03.6 mins

I can't give you more precise details that not how we publish the run-times.

https://www.apc.com/products/runtime_for_extendedruntime.cfm

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

mapc_apc
Crewman mapc_apc
Crewman

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

0 Likes
0
1854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 01:01 AM . Last Modified: ‎2024-03-19 02:37 AM

Thank you Gavan, very much appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore