Hello.
Can I connect my devices to an APC UPS using an IEC C14 to 4 Way Gang UK Mains Sockets Lead like the attached and the below:
https://images-na.ssl-images-amazon.com/images/I/71jRheuOJlL._AC_SX679_.jpg
Of course the load of all my devices will not exceed the total load of the UPS.
I ask because I was checking this page and I would like to have confirmation before proceeding with the setup I have in mind:
https://www.se.com/us/en/faqs/FA158852/
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:01 AM . Last Modified: 2024-03-19 02:37 AM
Provided the 4 way adapter doesn't have any surge protection and operates as a straight cable then your should be okay.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:01 AM . Last Modified: 2024-03-19 02:37 AM
Provided the 4 way adapter doesn't have any surge protection and operates as a straight cable then your should be okay.
-Gavan