Posted: 2024-07-01 11:47 PM
After I’ve changed my battery, the installation date isn’t changed automatically. Hiw can I change it manually?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-02 06:35 AM . Last Modified: 2024-07-02 06:36 AM
Disconnect the battery connector and wait for the system to declare a fault. Wait another 30 seconds, than reconnect the battery connector.
The system should prompt you to confirm this is a new battery. Toggle the LCD to (Yes) and enter the month / year than select save / enter.
Once complete initiate a manual self test.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-02 06:35 AM . Last Modified: 2024-07-02 06:36 AM
Disconnect the battery connector and wait for the system to declare a fault. Wait another 30 seconds, than reconnect the battery connector.
The system should prompt you to confirm this is a new battery. Toggle the LCD to (Yes) and enter the month / year than select save / enter.
Once complete initiate a manual self test.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-02 06:58 AM
It works. Thank you very much
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-02 07:33 AM
Great to hear - Rock On! 🤟