Have an older 1500 which threw a replace battery error. (Old battery was just over 2 years.) Managing the UPS with Powerchute Buz (PCB), current version. Updated the date of the battery in PCB, waited for the battery to come up to 100% charge, and verified the charge level in both PCB and the status lights. Pulled the wall plug, and my computer immediately shut off, (35% load indicated in PCB), no UPS function at all, just power off.
Restarted the UPS, showed 60% charge, and let it come back up to 100%. Then tried to do a calibration in PCB and had the same result, computer immediately shut down. Any idea what is going on?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:20 AM
Ha! I'm clearly showing my age 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:20 AM
Hi Gerald -
Have you attempted a self test? If so - what happens? You can initiate a self test via Powerchute or by pressing and holding the ON button (Probably labeled I/Test) on the front of your UPS. Once the UPS switches to battery you can let go.
It would also be helpful if you could supply the exact model and serial number of the UPS as well as what load is attached.
Thanks
Liam
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:20 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:20 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:20 AM
Thanks for the additional info. The UPS should certainly be able to support a Powermac and a cinema display without issue. I'm not sure how long you allowed the battery to charge, but I would suggest charging for at least 24 hours and then re-running the self test. Assuming that still fails, it sounds like the battery is bad. If it is a genuine APC replacement battery we offer a 1 year warranty on the battery itself. Tech Support could assist you with an exchange. Now if the battery is not faulty and has been allowed to charge the other possibility is that the charger is faulty. Usually a self test will catch this and you will get multiple LED's blinking in unison instead of just a replace battery LED. That being said, this UPS is 10 years old and that's definitely towards the end of its life expectancy.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:20 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:20 AM
It charged for over 24 hours. After trying another self test (it failed) I'm gong to return the battery.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:20 AM
Powermac is a blast from the past! Maybe it's a Mac Pro 3,1?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:20 AM
Ha! I'm clearly showing my age 🙂
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.