Hi,
We have a Smart-UPS RT 10000XL.
We had the batteries replaced a few days ago.
It seemed the batteries started charging right away but these messages remained:
"Discharged battery" & "The battery power is too low to support the load, if power fails, the UPS will be shut down immediately".
A while after the replacement the "battery capacity" showed 100% but when I run a runtime calibration it immediately drops to 6-7 %, after some hours it's back at 100% but still messages stay...
Please advice on what could be causing this.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:20 AM
Hello -
Your issue is most likely related to the UPS needing to be calibrated after the battery replacement. If the software or NMC initiated calibration is not running for the full runtime, you will likely need to perform a manual calibration. Info on this can be found in FAQ #FA156538, which you can find here:
http://www.apc.com/id/en/faqs/FA156538/
Liam
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:20 AM
Hello -
Your issue is most likely related to the UPS needing to be calibrated after the battery replacement. If the software or NMC initiated calibration is not running for the full runtime, you will likely need to perform a manual calibration. Info on this can be found in FAQ #FA156538, which you can find here:
http://www.apc.com/id/en/faqs/FA156538/
Liam
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.