Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2806:34 AM. Last Modified: 2024-03-1801:20 AM
Smart-UPS RT 10000 XL "Discharged Battery" Alert
Hi,
We have a Smart-UPS RT 10000XL.
We had the batteries replaced a few days ago.
It seemed the batteries started charging right away but these messages remained:
"Discharged battery" & "The battery power is too low to support the load, if power fails, the UPS will be shut down immediately".
A while after the replacement the "battery capacity" showed 100% but when I run a runtime calibration it immediately drops to 6-7 %, after some hours it's back at 100% but still messages stay...
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2806:34 AM. Last Modified: 2024-03-1801:20 AM
Hello -
Your issue is most likely related to the UPS needing to be calibrated after the battery replacement. If the software or NMC initiated calibration is not running for the full runtime, you will likely need to perform a manual calibration. Info on this can be found in FAQ #FA156538, which you can find here:
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2806:34 AM. Last Modified: 2024-03-1801:20 AM
Hello -
Your issue is most likely related to the UPS needing to be calibrated after the battery replacement. If the software or NMC initiated calibration is not running for the full runtime, you will likely need to perform a manual calibration. Info on this can be found in FAQ #FA156538, which you can find here: