Smart UPV VT 30kVA Unable to go out of bypass

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPV VT 30kVA Unable to go out of bypass
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
3
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

Smart UPV VT 30kVA Unable to go out of bypass

Hello,

We have one Smart UPS VT 30kVA. It is in bypass mode (static bypass mode), but when we try to go to normal mode it says "Unable to go out of bypass mode". The lever behind the panel is off/open, the input voltage is correct in the 3 phases, the load is 65%. We don't what can be the problem, maybe the batteries or the power module?

Thanks for your help

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
0
1402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

Hello,

I did some checking on this with our 3 phase tech support. We are not yet sure why it won't come out of bypass based on what you've said. It could be bad batteries, a power module issue (although that is less likely), a sensing issue with the Q7 breaker (internal maint. bypass), or pretty much anything. We would suggest contacting your local technical support for assistance. We would want to look at the raw status data the unit reports to find out why it's in bypass and also take a look at the active alarms/UPS log.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
0
1402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:26 AM

Hi,

I went back to our 3 phase support team and they told me this:

The raw status translates to:

  • Inverter IGBT L1 PM2 fault
  • Inverter relay/fuse L1 PM1 fault
  • Inverter IGBT L2 PM2 fault

That's bad news - you can try re-seating the power module (which might clear any false data) but failing that, the PM would probably need to be replaced. Also, since this UPS has not been charging the batteries, the batts may need to be replaced too (depending on their age and how long the UPS has been in this state). That would explain why it drops the load when there is a utility failure.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
0
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:57 AM . Last Modified: ‎2024-03-19 12:26 AM

Hello,

I did some checking on this with our 3 phase tech support. We are not yet sure why it won't come out of bypass based on what you've said. It could be bad batteries, a power module issue (although that is less likely), a sensing issue with the Q7 breaker (internal maint. bypass), or pretty much anything. We would suggest contacting your local technical support for assistance. We would want to look at the raw status data the unit reports to find out why it's in bypass and also take a look at the active alarms/UPS log.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
0
1402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:26 AM

Hello Angela,

Thanks for the fast answer. In the UPS faults log there is recorded a "System failure detected by surveillance", and the RAW data is M States = 09 02 02 00000638 00000480 00000001

Another thing, probably related, is that the UPS doesn't supply the load whe the power goes off. But the problem comes in when the power comes back again the UPS is in normal operation and is not supplying the the load, so we need to change to bypass. To avoid this problem we tried setting the bypass switch into on or closed so we dont need to change to bypass manually when the power comes back. But when setting the bypass switch the UPS stops supplying the load, so the inly way to do it is by setting the static bypass each time the power goes on and off.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
0
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:26 AM

Hi,

I went back to our 3 phase support team and they told me this:

The raw status translates to:

  • Inverter IGBT L1 PM2 fault
  • Inverter relay/fuse L1 PM1 fault
  • Inverter IGBT L2 PM2 fault

That's bad news - you can try re-seating the power module (which might clear any false data) but failing that, the PM would probably need to be replaced. Also, since this UPS has not been charging the batteries, the batts may need to be replaced too (depending on their age and how long the UPS has been in this state). That would explain why it drops the load when there is a utility failure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore