Smart UPS units will not power on

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS units will not power on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
121
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

0 Likes
9
1146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

Smart UPS units will not power on

My firm has 4 UPS units that will not power on. 2xSU1400RM2U and 2xSU1500RM3U. I know that the batteries are likely shot in all of the units. I have read on these forums that these units will not power on if the batteries are dead. While these are shot they do carry some voltage. How much voltage is necessary to get the unit to power on? Also, if the batteries are the issue and prevent the unit from powering up would any of the LEDs on the unit light?

Thanks
Steve

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

0 Likes
0
1146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

I finally decided to take a voltmeter to the same exact unit that we have in our lab.

It read 27.66 VDC.

So they're definitely a 24VDC system.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

0 Likes
0
1146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

This is the best bit of info here on these boards about these UPS's in general.
I had a DEAD Smapt UPS 2200net and i could net get it to respond in any way shape or form.
had replced the resistors,R38 & R43 with 1k and Caps C34 & c35 22uf 16v
and still nothing. then I charged up the caps through the battery connections, the one in front and the one in rear,
with a alligator clip wire bridging both in series, (just like the big yellow wire does when batteries are connected)..
and BAM...Came to LIFE. Started trying to charge the batteries that weren't there.
kept running too. this is a great test to verify things are working. Heck i don't wanna spend $200 on batteries if they aint gonna work.

Boooooooooooooooooooooooo
to APC for NOT supplying any info to a whole bunch of very qualified techs on this board, and NOT supplying schematics
or any kind of tech support. Its bull crap.
you guys know you had a engineering issue with those resistors, and did nothing about it.
Im surprised there was no class action lawsuit brought against you for it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

0 Likes
0
1146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

I was wondering about the configuration of those batteries. Depending on the wiring 12v, 24v or 48v were all possible. What is the configuration for a SU1400RM3U Smart-UPS? If I was a betting person I would say it too was 48v.

Steve

Message was edited by: ilecoder

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

I believe the lowest threshold for the batteries is somewhere between 16 and 18VDC. With a bad set of batteries, the ONLY LED that may illuminate on the UPS is the Site Wiring Fault (if one exists). The rest of the panel will not light.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

I have the 2xSU1400RM2U at home with me. I pulled the battery tray and attempted to force a charge into the four small SLA batteries. One battery is holding at 8v, another battery is reading 7.2v, and the last two read around 6v. I doubt that these voltage readings would hold up if any type of load is placed on them.

I am just attempting to prove if the units function and justify new batteries.

I think I am going to suggest that one battery cartridge be purchased and that if both units can be shown to work off that one unit that another cartridge could be purchased.

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

The control module requires presence of voltage across the battery terminals before activating anything.

There is a set of large capacitors at the battery connection. You should be able to feed the battery terminals with a 12-15v DC adapter,which will actually charge up the capacitors to 15-20v. Give it about a minute to "charge up" the capacitor, then disconnect the wallwart. Measure the voltage across the battery terminals. You should see the voltage retained by the capacitor. After you check the presence of 15-20v, you should be able to plug in the UPS and turn it on.

It will turn on then immediately shut off as it attempts do a self-check and transfer to battery power.

If you can duplicate this, I would go ahead and try a new battery. I don't think you'll have any trouble finding a 12-15v wall-wart around the office. Just make sure the output is DC and observe the polarity.

Also, are you going to be putting all four units into service within the next month or so? If not, only order replacement batteries for units that you will be using right away. If you replace the battery and put the units back in storage for later use, you'll just ruin them again.

Edit:

RBC24 is 12v 8 or 9Ah x 2 in series and two strings of them in parallel forming a 24v 16/18 Ah battery pack.

Message was edited by: KVAr

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

KVAr, I tried the trick with my SUA1500I and it worked! At least now I know only the batteries need replacing, not the whole unit. Thanks for a good advice, mate!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

KVAr

I opened up one of the SU1400RM units - it's actually a DL1400 which means that it was purchased from Dell. The wiring harness tells me that the four batteries are configured as 24v at 16ah. The original batteries are four 12v, 8ah batteries.

I have to believe that the SU1400RM2U units have a similar battery arrangement since they do use the same battery - just in a tray configuration. I do not understand why the batteries were glued into the tray.

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

All microprocessor controlled Smart UPSs are like that. Unlike the older Back-UPSs, battery voltage is required. So, I think buying one battery pack or the aforementioned wall wart trick should do.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:44 AM . Last Modified: ‎2024-03-08 02:01 AM

I finally decided to take a voltmeter to the same exact unit that we have in our lab.

It read 27.66 VDC.

So they're definitely a 24VDC system.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of