Smart-UPS not holding charge level

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS not holding charge level
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:14 AM . Last Modified: ‎2024-03-07 11:22 PM

0 Likes
3
1640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:14 AM . Last Modified: ‎2024-03-07 11:22 PM

Smart-UPS not holding charge level

Hi.

I've got a Smart-UPS 750 (DLA750I) which has an issue maintaining charge. I changed the battery pack, but issue persists. Here's what happens:

1. Installing new batteries. UPS starts recharging up to 100%.
2. It steadily reports 100%.
3. Next scheduled self-test it beeps due to batteries being discharged (and sometimes also causes a power cut on equipment attached to it)
4. Starts recharging up to 100%. This repeats.

If I let it charge up and leave it for a day, it will report 100%. I run a self-test, and it'll then report the battery charge to 20% (or whatever, depending on load). It'll then charge back up to 100% and then let them drain (without changing the reported charge level).

So basically, the only way to have the batteries "topped up" is to run the self test repeatedly. Anyone else come across this issue and if so, is there a way to fix it?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • charge
  • dla750
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-06-30 07:14 AM . Last Modified: ‎2024-03-07 11:22 PM

0 Likes
0
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:14 AM . Last Modified: ‎2024-03-07 11:22 PM

What happens if you charge the batteries to 100% then unplug them, and a day or two later, plug them back in and then run off battery?  If the batteries are in good condition then they will still run for the expected run time, but if you have one or more bad batteries in the pack, they'll lose their charge even when they are unplugged for that day.

Bad batteries will often work well just after they have charged, but they can't hold the charge for very long and will go flat even if they are unplugged and not being used.  A good battery will be able to be unplugged even for a few weeks without losing much in the way of a charge.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-06-30 07:14 AM . Last Modified: ‎2024-03-07 11:22 PM

0 Likes
0
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:14 AM . Last Modified: ‎2024-03-07 11:22 PM

Yes this happens when the batteries are almost dead.  If your batteries are new you'll have to return them for replacement as it means before you bought them they were sitting on a shelf for so long they went flat and were damaged and now can no longer hold a charge properly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:14 AM . Last Modified: ‎2024-03-07 11:22 PM

0 Likes
0
1641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:14 AM . Last Modified: ‎2024-03-07 11:22 PM

That was my initial thought as well. However, If I do a self-test, let it charge back up to 100% and then cut the power, the equipment I have connected stays on battery power for the expected amount of time. So it would seem the batteries are able to hold a charge. I've changed packs twice.

Reply

Link copied. Please paste this link to share this article on your social media post.

Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-06-30 07:14 AM . Last Modified: ‎2024-03-07 11:22 PM

0 Likes
0
1642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:14 AM . Last Modified: ‎2024-03-07 11:22 PM

What happens if you charge the batteries to 100% then unplug them, and a day or two later, plug them back in and then run off battery?  If the batteries are in good condition then they will still run for the expected run time, but if you have one or more bad batteries in the pack, they'll lose their charge even when they are unplugged for that day.

Bad batteries will often work well just after they have charged, but they can't hold the charge for very long and will go flat even if they are unplugged and not being used.  A good battery will be able to be unplugged even for a few weeks without losing much in the way of a charge.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.