Smart UPS X1500 - On battery power in response to an input power problem.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS X1500 - On battery power in response to an input power problem.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
mkuhn22
Ensign mkuhn22
Ensign

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

0 Likes
7
2986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

Smart UPS X1500 - On battery power in response to an input power problem.

Hello - 

  I am regularly having the above device alarm on a newly installed Smart UPS X1500.  When this happens no power event is appearing to take place.  In fact, I have an older Smart UPS 1000 plugged into the same outlet group that does not throw any alarms at the same time.  I have attached the logs of the chatty X1500 and the 1000 plugged into the same outlet group for comparison.  Any help is certainly appreciated!

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

0 Likes
0
2986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

Good thing I got a StruxureWare Data Center Expert training last week! So you're getting ALL of your notifications from DCE, right? Not the devices themselves?  (if you have a screenshot of one, I can verify) Are they emails, traps, etc? I wasn't sure what you had but assumed email.

And we are talking about actions you have set up under Alarm Configuration->Create Notification Policy and alarm actions defined there? From looking at this screen, it seems like the most granular level we can modify the notifications is at the group level. On the UPS/management card itself, we can modify specific events/alerts and delay them, etc.

Thank you for the log files. Looking at them seems to confirm no notifications are set up on them specifically.

The SMX1500 is very new so that rules out an old firmware issue I was thinking of. It does have a sensitivity setting you can try changing via the web interface under Configuration->Power Settings and try changing it down from Normal (what it is set to now) to Reduced and if that doesn't help, try it on Low and apply that and observe. I do not see any glaring problems in the data log. 

But, both units are set to Normal currently. They are different models but on different firmware versions. Both of them are not at the latest versions I noted.

I think you should try adjusting the sensitivity setting on the one first, see if any change, as it is the simplest option. After that, I would want to pursue a UPS firmware upgrade - which unfortunately cannot be done through DCE - but can be pushed via the Network Management Card in the UPS to the UPS itself. Though, the major caveat is that the UPS power output needs to be turned off when doing the upgrade. I can give more details on that if we decide and are able to go that route. I didn't see anything flat out explaining this specific issue in the UPS firmware release notes but general references to tweaking UPS behavior.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
mkuhn22
Ensign mkuhn22
Ensign

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

0 Likes
0
2986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

Hey all, was wondering if anyone had seen anything in the logs to indicate what the issue is?  We've basically had to stop monitoring this device thanks to the amount of false positives it's throwing. 

 

Assuming nothing can be seen in the logs is there any way to adjust the sensitivity of the device, or to possibly set the device to only alarm if on battery power for more than ~5 seconds?

 

Again, any information is greatly appreciated.  Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

0 Likes
0
2986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

Hi Michael,

Can you provide the full .tar file from About->Support menu from each UPS's web interface? I am looking to check some other detail not available in the log files you've already shared.

These UPSs, once I confirm some details, are likely two different platforms/models and may have different sensitivity settings, etc so they could be reacting differently to little power fluctuations not apparent to the naked eye.

Each UPS does have power quality and/or sensitivity settings that can be adjusted. The network management cards also offer the ability to adjust how email notifications are handled which means you can delay them unless the event lasts for X seconds/minutes. You'll find the ability to do that under Configuration->Notification->Event Actions->By event and look under Input Line status events for this one, click on it, and then click on each recipient receiving it to tweak the delay/notification settings for it while we sort this out. I do not recommend you disable it from the event logging, just delay how email and/or SNMP trap receivers get notified. Let me know if any questions on this part.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

0 Likes
0
2987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

Good thing I got a StruxureWare Data Center Expert training last week! So you're getting ALL of your notifications from DCE, right? Not the devices themselves?  (if you have a screenshot of one, I can verify) Are they emails, traps, etc? I wasn't sure what you had but assumed email.

And we are talking about actions you have set up under Alarm Configuration->Create Notification Policy and alarm actions defined there? From looking at this screen, it seems like the most granular level we can modify the notifications is at the group level. On the UPS/management card itself, we can modify specific events/alerts and delay them, etc.

Thank you for the log files. Looking at them seems to confirm no notifications are set up on them specifically.

The SMX1500 is very new so that rules out an old firmware issue I was thinking of. It does have a sensitivity setting you can try changing via the web interface under Configuration->Power Settings and try changing it down from Normal (what it is set to now) to Reduced and if that doesn't help, try it on Low and apply that and observe. I do not see any glaring problems in the data log. 

But, both units are set to Normal currently. They are different models but on different firmware versions. Both of them are not at the latest versions I noted.

I think you should try adjusting the sensitivity setting on the one first, see if any change, as it is the simplest option. After that, I would want to pursue a UPS firmware upgrade - which unfortunately cannot be done through DCE - but can be pushed via the Network Management Card in the UPS to the UPS itself. Though, the major caveat is that the UPS power output needs to be turned off when doing the upgrade. I can give more details on that if we decide and are able to go that route. I didn't see anything flat out explaining this specific issue in the UPS firmware release notes but general references to tweaking UPS behavior.

Reply

Link copied. Please paste this link to share this article on your social media post.

mkuhn22
Ensign mkuhn22
Ensign

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

0 Likes
0
2986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

Angela -

  Thanks again for all the info!  Yes, we get all of our notifications from DCE, a one stop shop to manage our 60ish devices.  Indeed, I didn't see any way to get more granular within DCE either. 

  I have changed the sensitivity on the X1500 to reduced to see if that makes a difference.  If not I will adjust again to low and try.  I will let this sit for a few days and will follow up. 

 

Thanks again for your time!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

0 Likes
0
2986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

You're very welcome.

Reply

Link copied. Please paste this link to share this article on your social media post.

mkuhn22
Ensign mkuhn22
Ensign

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

0 Likes
0
2986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

Angela -

  I just wanted to follow up.  Since making the change we have seen a marked decrease in false positives.  We've still had a couple, but the numbers are significantly lower than before.  This adjustment has made all the difference.  Thank you again for your support.  We will probably go ahead and move both devices to the lowest sensitivity just to completely put the problem to bed.

Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

0 Likes
0
2986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:25 PM . Last Modified: ‎2024-02-29 11:57 PM

Hi Michael,

Glad to hear. You're very welcome!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of