The UPS goes on battery when the input voltage is not in range or cannot be corrected by the AVR of the SMX unit I suggest check your input voltage if the voltage is different from the set output of the UPS reduce sensitivity the SMX units is normally on the highest sensitivity by default
You can also change the High and low transfer point when using the advance menu type