Smart-UPS X SMX1000C keeps jumping from grid to battery - VIDEO
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-1503:38 AM
The UPS goes on battery when the input voltage is not in range or cannot be corrected by the AVR of the SMX unit I suggest check your input voltage if the voltage is different from the set output of the UPS reduce sensitivity the SMX units is normally on the highest sensitivity by default
You can also change the High and low transfer point when using the advance menu type
If the voltage is normal and you already have the lowest sensitivity and other UPS are working normally on the same circuit the UPS may have faulty sensors and may need to be replaced