Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Smart-UPS X 3000: Power Factor Correction Fault after losing input power

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS X 3000: Power Factor Correction Fault after losing input power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Andy_acc_apc
Andy_acc_apc
Cadet

Posted: ‎2021-06-30 07:21 AM . Last Modified: ‎2024-03-07 11:10 PM

0 Likes
0
1789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:21 AM . Last Modified: ‎2024-03-07 11:10 PM

Smart-UPS X 3000: Power Factor Correction Fault after losing input power

After losing input power to this UPS, it now won't power on correctly again. The warning led becomes red, all others are off.

 

We have a management card attached and can access it. We see the warning message A power factor correction fault exists.

 

This prevents me from turning output power on or running a self test.

 

When I try to turn the UPS off and on again, it comes back to the same state, and the logs say:

Model
Smart-UPS X 3000
 2 Critical Alarms Present
  • The output power is turned off.
  • A power factor correction fault exists.
 3 Warning Alarms Present
  • The power for switched outlet group 1, Outlet Group 1, is off.
  • The power for switched outlet group 2, Outlet Group 2, is off.
  • The power for switched outlet group 3, Outlet Group 3, is off.

Current input voltage seems to be normal: Input Voltage: 226.5  VAC @  50.0  Hz

cli status:

apc>ups -st
E000: Success
State: Off, PFC Fault

apc>detstatus -all
E000: Success
Status of UPS: Off, PFC Fault
Last Transfer: None
Input Status: Pending acceptable
Next Battery Replacement Date: 07/07/2024
Runtime Remaining: 18 hr 12 min 15 sec
Battery State Of Charge: 99.9 %
Output Voltage: 0.0 VAC
Output Frequency: 0.0 Hz
Output Watts Percent: 0.0 %
Output VA Percent: 0.0 %
Output Current: 0.00 A
Output Efficiency: output off
Output Energy: 0.000 kWh
Input Voltage: 226.5 VAC
Input Frequency: 50.0 Hz
Battery Voltage: 130.8 VDC
Battery Temperature: 18.3 C, 64.9 F
Self-Test Result: Unknown
Self-Test Date: 03/02/2021
Calibration Result: Unknown
Calibration Date: 03/02/2021

 

Any idea, can we fix this quickly?

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore